Bit of advice please. Not too used to this stuff.
In large old building, a couple of MICC radial circuits feeding a few sockets each. All tests pass, all RCD protected, very good Zs etc.
Questions:
My initial hunch is C3 for 1st one as it would require effort to make it dangerous and C2 for 2nd one.
Thanks.
In large old building, a couple of MICC radial circuits feeding a few sockets each. All tests pass, all RCD protected, very good Zs etc.
Questions:
- chassis of metal consumer unit being used for CPC, no banjos/fly leads etc. It clearly works very well but should there be a banjo / pyro clamp really?
- all 12 sockets have no earth fly lead from metal surface box to front. Again metal box used for cpc. So cpc to socket relies on case making good connection and the 2 screws. Easily solved of course.
My initial hunch is C3 for 1st one as it would require effort to make it dangerous and C2 for 2nd one.
Thanks.