Right chaps had a spooky one to day ,Periodic inspection of a church ,complete with coffin ,(funeral later in the day ) right refused to carry out some of the tests due to the respect value , but heres the crunch mims metal clad DB mims in mims out top and bottom all sockets metal clad mims in , installation is 55 years old but testing out ok , as youd expect with pyro , problem is the ring main L N continuity fine 0.48 on each , but its a metal clad DB and metal Clad back boxes and only an inch of exposed pyro so and cpc readings will be incorrect , so i have dont 2 R1 R2 tests and measured from the furthest points , insulation reading were >200 M so no probs any thoughts