B

BigD76

Hi guys I have a garage which has 2 double sockets, 1 spur for a electric door and 2 single 5 ft fluorescent lights what's would be the ideal cable size for a supply. As its currently powered by a 1.5 T&E radial run outside from the main board unprotected under decking and up the wall......not done by me by the way.
 
25m of 2.5mm @25A ( it's current ratingf) will be outside VD limits for lighting.. anything over 15A you will need 4mm or 6mm.
 
Use your cable calcs in association with the load you calculate not forgetting to apply diversity ... you have given us very little info about the cable, proposed installation methods as well as expected loads on the sockets i.e. dryer, heater just general small loads etc ....... as you are asking the question I assume you want to install it but seem to have missed all the relevant info we require so brings the question of your competence in doing so can you show your calculations that way we know you have a grasp of the task your undertaking and we can make any minor corrections if needed and we know you will then be competent to install a safe circuit.
 
Hi guys I have a garage which has 2 double sockets, 1 spur for a electric door and 2 single 5 ft fluorescent lights what's would be the ideal cable size for a supply. As its currently powered by a 1.5 T&E radial run outside from the main board unprotected under decking and up the wall......not done by me by the way.


Theres the minimum and then theres allowing for the future, if your own house I would install a 4 way distribution board in the garage and have 1 20 AMP Radial circuit for the sockets and 1 6 amp for the lighting with 2 spare ways, as for the size of cable again if my own garage I would install a 3 core 10mm2 armoured on a 40 amp supply, however after all that if you want to do the job on the cheap I would feed the 2 sockets via a 4mm2 radial and also feed a spur unit off them to feed the light, JMO
 
The problem is the house is only 5 months old so how has this been signed off surely a 1.5 radial to feed a gargle electric door 2 lights and 2 twin sockets is not allowed.
 
it is allowed if you are mr.diy (spelt divvy) and don't bother with certs. paperwork don't make the lights come on any brighter. :2guns:
 
Is it done in 2.5 grey T&E pvc clipped up garage as this probably wont be UV tolerant and will show signs of breakdown within 5yrs depending on direct sun or not... also I assume at 5months it is rcd protected... what is the whole circuit set up from fuse to garage.
 
The problem is the house is only 5 months old so how has this been signed off surely a 1.5 radial to feed a gargle electric door 2 lights and 2 twin sockets is not allowed.


If the house is only 5 months old, then the whole place is still under guarantee. Write up a report for the customer, and have them give it to the builder, or send it off to the builder, if they are no longer on site!! Simples!! lol!!
 
If the house is only 5 months old, then the whole place is still under guarantee. Write up a report for the customer, and have them give it to the builder, or send it off to the builder, if they are no longer on site!! Simples!! lol!!

Is the OP the customer?

If this is a 5 month old install, the sparks need a kick up the backside. VERY bad install IMHO.


Makes you wonder whats under the floor!
 
Is the OP the customer?

If this is a 5 month old install, the sparks need a kick up the backside. VERY bad install IMHO.


Makes you wonder whats under the floor!

Doesn't really matter, if it's the OP's house, if it is, then he sends his own report to the builder!! lol!! Either way, the garage installation doesn't comply with either past or the latest Reg's.

New builds have always been notorious for using bottom of the barrel sparks. These day's it'll probably be Electrical Trainee's doing the installs!! lol!!
 

Reply to min cable size for garage connect in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
153
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
509
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
457

Similar threads

Sounds more positive.
Replies
8
Views
592
  • Question
Passing through the wall should be in conduit to protect the cables. Yes cables should be clipped.
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top