Hi everyone, quick question. In the OSG it states minimum tails from the meter and supply head must be 25mm. Now lets say there's a flat on the third floor and the current tails are 16mm. Would this then mean that the they would need to be replaced making damage all the way up a communal halway up three floors, meaning its going to cost a customer considerably more just to bring a board up to scratch if a new board was being put in. I have someone telling me the abadiatic equation will prove it can stay 16mm and another saying no, no ifs no buts it must be 25mm. Whats the deal here? Opinions?
 
if the fuse protecting those 16mm tails is 60A or 80A then they're OK to remain. adiabatic needs to be done to calculate the size of the earthing conductor. it's new installations where 25mm should be used.
 
Quick addition, yes I have said OSG says, but I have been told OSG is maximum measured values and to stick to to be 100% safe and in reg. And that the Regs is tabulated values and therefore more accurate and specific. So please if you feel like saying "you just said OSG says"... please dont. Id like constructive feed back and im not trying to engineer this so I get the answer I want. Im just looking for constructive feedback wiith explanations not quippy answers with things like "the answer is in the question" etc... Thanks
 
Quick addition, yes I have said OSG says, but I have been told OSG is maximum measured values and to stick to to be 100% safe and in reg. And that the Regs is tabulated values and therefore more accurate and specific. So please if you feel like saying "you just said OSG says"... please dont. Id like constructive feed back and im not trying to engineer this so I get the answer I want. Im just looking for constructive feedback wiith explanations not quippy answers with things like "the answer is in the question" etc... Thanks
Please don't take this the wrong way, but Tel has given you the answer fella.
 
Both Tel and MDJ are right in what they say. But if youre fuse is 80a or lower, then the 16mm tails are fine.

the adiabatic is the best way to calculate the size of the main earthing conductor, but if we look a bit deeper into the regs, we can do it by another formula, and to cut a long story short, you can use a main earthing conductor that has a minimum CSA of 50% of your tails, so in your case 10mm would be the best fit. It is covered in parts 4 and 5 of the regs.

Cheers.................Howard
 
Hi everyone, quick question. In the OSG it states minimum tails from the meter and supply head must be 25mm. Now lets say there's a flat on the third floor and the current tails are 16mm. Would this then mean that the they would need to be replaced making damage all the way up a communal halway up three floors, meaning its going to cost a customer considerably more just to bring a board up to scratch if a new board was being put in. I have someone telling me the abadiatic equation will prove it can stay 16mm and another saying no, no ifs no buts it must be 25mm. Whats the deal here? Opinions?

If this CU has been in use for a number of years, with absolutely no detrimental signs etc why would you even be thinking or considering changing 16mm for 25mm tails, if the cut out fuse is known to be 60/80A??
Because it say's so in an OSG (the G standing for Guide)? More fool you, because it say's nothing about minimum tail size in BS7671

How is the adiabatic equation being brought into this, that equation is to size main earthing conductor, rather than the supply tails...

If i were supplying tails for a new installation that had a DNO fuse rated at 60A, i can tell you now, i would not be providing 25mm tails!!
 

Reply to Minimum CSA Tails? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top