liam b
when you do a job which is say a spur off the ring in the living room but the customer wont have there earth bonding upgraded what do yous do?
cheers
cheers
Last edited by a moderator:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Minor works and bonding in the Australia area at ElectriciansForums.net
I'm asking to confirm...
Main bonding must be in place before any work is carried out, Minor Works or other.. Correct?
If TN-CS then any electrical work must comply to BS7671 (17th ed) & requires the bonding to be 10mm (if the neutral conductor is less than 35mm, Table 54.8) So if 6mm, this needs upgrading what ever the type of work in any location...Correct?
If TN-S or TT then any electrical work must comply to BS7671 (17th ed) & requires the bonding to be not less than half the CSA of the earthing conductor and not less than 6mm. So if you had a 6mm or 10mm earthing conductor then a 6mm bonding conductor would be acceptable... Correct?
An example..
A customer would like new downlighters installed to the bathroom.
It is a TN-CS supply
bs3036 rewireable Fuse board
They have a 6mm main earth and 6mm bonding to gas and water services..
The solution to this would be to provide 30ma RCD protection to the addition/alteration or the whole circuit.
Upgrade the Bonding to 10mm....correct?
If a TN-S or TT this situation would of only required RCD protection, earthing and bonding fine as is.....Correct?
No matter what size of works if bonding and main earthing is lacking or insufficient then its got to be addressed. Reg's require it. NICEIC require it and so should you. Its up to you as the competent person to educate the client as to the importance of earthing and bonding. If they still refuse then I have to agree with a previous post you need to walk away. If you carry out the works it could possibly come back and bite you.
An apprentice has shown me this from esc.org website questions and answers
Can anyone else confirm 6mm is ok on PME, when you look at the regulation in the book it doesn't say anything at all about 6mm can stay, I've always upgraded to 10mm on PME, and this apprentice is telling me I don't need to...Look at this he says... (Contradicts its self to me)
Q2.12
When carrying out electrical work on an installation forming part of a TN-C-S system, is it necessary to upgrade existing 6 mm² protective equipotential bonding to 10 mm²?
Not necessarily. If the existing 6 mm² bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not require to be upgraded.
Regulation number(s) 132.16 544.1.1
Any scenarios where you'd change to 10mm then on a PME? or are there none?