minor works cert help | on ElectriciansForums
Discuss minor works cert help in the Australia area at ElectriciansForums.net
sinaloan
hi there i am filling in a minor works cert and in part 2 it asks for 'overcurrent protective device for the modified circuit' and 'residual current device'. i have a split load board with one rcd on it. the work has been carried out on a ring circuit on the rcd side so i assume i put in the rcd box i fill in the rcds details? in the 'overcurrent protective device for the modified circuit' box do i put in the mains switch bs number 60947-3 or do i put in the main fuse bs number 1361?
ahhhh ok now i see thanks very much guys. also a quick one i have changed a fuseboard and im filling in a domestic electrical installation certificate. when would the next inspection date be due? is it ten years? this is for my nic eic domestic installer application
Depends what installation it is Domestic, Commercial etc
what is your Ze and pfc as measured? don't forget . you measure Ze with main earth dissed and pfc with earths and bonds connected.
Maximum is normally dictated by the DNO's fuse max rating. I believe that the minimum recommended for them is around 16.5 KA Most main switches 60947-3 are rated up to 6 KA (and it should be marked on each BS standard compliant device).
yes thats great i understand the ze, zs, ir, cont tests etc and know why you do them and what all of the expected results should be and why but iv never understood pfc and what its about and what the reading should be or mean. my college were rubbish and i learnt more over the three years researching myself.
When measuring pfc you are attempting to ascertain what is the largest current your equipment could reasonably be expected to handle safely. In most domestic installations you are generally relying on the DNO main fuse for that (whatever type it is). You may want to "beef up" your CU if you get anything over 6 KA. Remember it may be a much higher potential current (and a probable problem) if you have a really good earth ie < 0.0139 Ohms.
telectrix my measured ze was .20 and my pfc was 1.25ka this installation is a tns so the ze measurement is ok. is the pfc? and how am i meant to know if its ok or not on other installations?
basically your pefc is the current you would get if there was a fault of negligible impedance ( dead short ) between L and E. using ohms law you woud expect I = V/R, or V /Ze. i.e. 230/0.35 ( taking the max. Ze for TNC-S ). = 657A . obviously, the values of V and Ze will vary.
Reply to minor works cert help in the Australia area at ElectriciansForums.net