ok cool, this will be the second attempt,
i have a circuit tested to be too high Zs Values for the existing protective divice, its an addition to an existing radial circuit, however the new addition is protected by a 13a spur, the max permitted Zs value for the BS1362 is acceptable.


my question is this! is it acceptable to use a BS1362 as the circuits overcurrent protective device for the modified circuit when completing a minor works cert, cant say I have never given it much thought until now????
 
Last edited by a moderator:
OK so the extra part of the circuit you have added from the 13 amp FCU sounds acceptable as long as the BS 1362 fuse will disconnect the circuit in 0.4 of a second the problem you have is that you have fitted the 13 amp FSU on the circuit that the OCPD supplying that needs to disconnected the circuit within 0.4 seconds if is does not then it is unsafe , If there is 30mA RCD protection you may be able to get away with it , but it Is not good practice just the really on an RCD for fault protection
 
looking at it logically, if the 1362 fuse will diss. in 0.4 secs for the extension part of the curcuit, and the Zs at the FCU is within the max. for the OCPD at the origin of the circuit, then it should comply. tin hat firmly on.
 
I agree with you Tele but if the Zs at the FCU is to high for the OCPD for that circuit then the OP has a problem

hi thanks for the reply, yes the Zs is well within at the point of the spur, its just the new circuit which is high, it will require investigation but should do for now.
 
so if its a new cicuit ,not an addtion or modification to a circuit then an installation cert may be required
Athough even saying it ,an eic seams over the top for such a small job , but thems the rules

I think the definition section of bs7671 is required here. Think it says a circuit starts at a fuse board our similar
 
Can't see any problem with that at all. list BS1362 as OCPD and list cable size from the load side of spur. If Zs is low enough for fuse rating and cable protected then it is definately ok.
 

Reply to minor works high Zs Values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
Replies
1
Views
249
On the minor works in the brown book it has Zdb
Replies
3
Views
296

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top