Insulation ressistance on a minor works cert is that the original circuit plus addition or only the addition say a spur ??
rich
rich
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss minor works insulation ressistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Insulation ressistance on a minor works cert is that the original circuit plus addition or only the addition say a spur ??
rich
Eeeerrrrrr u sure about that???
I assumed that too until i was put right that i was only testing the insulation res on the cable i had put down & only Zs the circuit. Also RCD test as normal.
S
Well you would test it like you test any other circuit IR, only you are not obliged to test the entire circuit but only the cables you have put in allowing L/N test aswell.
See i'm just telling you what ELECSA told me because i had a problem where i couldn't unplug every appliance or extension lead.
Hope that explains abit more
Testing IR from the start of the cable you have put in, strip the wires before terminating them(eg. as a spur) for any damage that may have occurred whilst you were installing them.
Same principle just not tested at the distribution board. Only testing the work we have done remembering we still do Zs & RCD test the whole circuit/installation