Fair enough you can do that.
This article sums up my opinion better than I could..
Majoring in the Minor Works Certificate - https://professional-electrician.com/technical/majoring-minor-works-certificate-napit/
R1+R2 is taken at every point for eic.I have a little confusion over MWC's.
Currently we are adding a lot of smoke detectors to rental properties due to the change in the law around HMO licenses. Often its just upgrading from a D LD1 to a D LD2 system type. On smaller properties its just taking permanent feed off a local lighting fixture and putting a smoke detector in the living area, which is usually being used as a bedroom. And then wiring to smoke detectors in all the bedrooms upstairs from the exsisting one on landing via loft.
When completing MWC's for this above work its is necessary to perform R1+R2 for every fixture on the lighting circuit? A lot of these places have 1 lighting circuit feeding both floors so performing R1+R2 at every point takes a while and all I'm doing is adding 1 smoke detector. Would it be acceptable to confirm R1+R2 at my new smoke detector and the fixture immediately after, as I have not done anything that will affect the circuit beyond this.
Edit: A word
Zs technically doesn't prove cpc continuity though it is a good indication.IMO, you would not need to perform R1+R2 testing. a Zs reading would confirm cpc integrity and that reading can be entered on your MWC.
I've heard that grade of alarm is supposed to be interconnected. Is that true? If so how are you doing it?
It would be odd not to use a rcbo unless you can jiggle something around upstream. No rcd = ra plus labels on sockets for specific use only. No?Going back to the op original question , here is an example i come acroos a lot , carry out an eicr and there is a 32 amp mcb protection a 2.5mm radial socket circuit on the 2nd floor of an office.
We are then ask to carry out remedial work, now do you .
A. downrate to a 20amp mcb.
B. downrate to a 20 amp rcbo.
It would be odd not to use a rcbo unless you can jiggle something around upstream. No rcd = ra plus labels on sockets for specific use only. No?
B.Going back to the op original question , here is an example i come acroos a lot , carry out an eicr and there is a 32 amp mcb protection a 2.5mm radial socket circuit on the 2nd floor of an office.
We are then ask to carry out remedial work, now do you .
A. downrate to a 20amp mcb.
B. downrate to a 20 amp rcbo.
You Can't use lables on sockets now to say for specific use , they stoped that with the 18thIt would be odd not to use a rcbo unless you can jiggle something around upstream. No rcd = ra plus labels on sockets for specific use only. No?
Just curious... Does your alarm system signal something if one of the devices drops of the network? If so do mind telling what brand/range you're using?It differs from house to house but we generally install radio link bases downstairs from existing light fixtures then replace the existing landing smoke with a radio link and hard wire from there to upstairs rooms via the loft.
Don't usually know where last point on circuit is, usually not too hard to figure it out though.
Am i the only one who minor works everything?
If i change a cracked lightswitch like for like i carry out a full range of tests and certify it.
Reasons are habit, and also do alot of work in social housing so always wanting to cover my back. Photo of every job also saved in the computer job file.
No hope of me issuing a MWC to change a cracked light switch. I doubt house owners issue themselves a MWC when they replace a light switch.
Do you also issue a MWC when you replace a customer's light bulb?