I did and i did.

Only on one tho.

Typical he chose that one, but he just confirmed what i said earlier.
:)

Reg 522.8.1(if we are being really picky) does not specifically say that they must be used.

"Failure to provide a grommet whare a cable, such as a twin and cpc flat cable, enters a metal black box is not, in its own right, a deficiency, providing the cable sheath is adequately protected against damage from any sharp edges."


fair enough, i wouldnt be that lucky. Ive had some right jobs worths
 
No code required then. :) The cables are in plaster and can't go anywhere. I still believe its poor practice. I have a printed copy of the ESC PIR Codes and there is nothing written about it. That's why I checked here. :D

Andy
 
Its good practise to fit them during installation
If there are none on an existing installationm and there is no sign of damage then there is no code
What are you people thinking when recomending a code for something like this You would probably incur more damage trying to have them fitted than ever would occur otherwise
Start thinking for yourselves instead of being guided blindly without common sense
 
Its good practise to fit them during installation
If there are none on an existing installationm and there is no sign of damage then there is no code
What are you people thinking when recomending a code for something like this You would probably incur more damage trying to have them fitted than ever would occur otherwise
Start thinking for yourselves instead of being guided blindly without common sense

If you read my post correctly you will see that I was told by my NICEIC inspector at my last inspection to code missing grommets as 2. Despite what I think I have to comply otherwise Mr NIC goes back to head office with a reccomendation for a another inspection in 6 months which then costs me, and if I still dont do it he goes back to head office again with a reccomendation for removal from the role of approved contractors.

Also there is nothing wrong with my thinking, and I have plenty of common sense.:mad:
 
Last edited by a moderator:
What are you people thinking when recomending a code for something like this You would probably incur more damage trying to have them fitted than ever would occur otherwise
Start thinking for yourselves instead of being guided blindly without common sense

People come on the forum for advice and guidance in situations that they may be unfamiliar with.

I dont think there is any need for posts like this.

Its a discussion, not an ear bashing.
 
What are you people thinking when recomending a code for something like this You would probably incur more damage trying to have them fitted than ever would occur otherwise
Start thinking for yourselves instead of being guided blindly without common sense

Maybe you could provide a full list of official PIR codes to eliminate any confusion?

It doesn't mean that people are not thinking for themselves because they are asking what other electricians would do in a particular situation. This is what the forum is all about.

Common sense should tell you that posting comments like 'start thinking for yourselves' to qualified people isn't going to go down very well. :mad:
 
Maybe you could provide a full list of official PIR codes to eliminate any confusion?

It doesn't mean that people are not thinking for themselves because they are asking what other electricians would do in a particular situation. This is what the forum is all about.

Common sense should tell you that posting comments like 'start thinking for yourselves' to qualified people isn't going to go down very well.

My sincere and humble apologies for the way the reply came over

In all honesty it wasn't meant to slag off or demean anyone

My snap reply was meant more to encourage the individual to assess the current danger, rather than code the bad practise which I believe may cause greater danger when trying to rectify (The think for yourself line was not justified when reread by myself )
I am far from being a know it all and enjoy giving an opinion and recieving contrary opinions
Sorry for any offence to any of the previous contributors
 
I did and i did.

Only on one tho.

Typical he chose that one, but he just confirmed what i said earlier.
:)

Reg 522.8.1(if we are being really picky) does not specifically say that they must be used.

"Failure to provide a grommet whare a cable, such as a twin and cpc flat cable, enters a metal black box is not, in its own right, a deficiency, providing the cable sheath is adequately protected against damage from any sharp edges."
"in its own right"--of course meaning alternatives are also acceptable,why not bring the conduit into the box?De burring might work.The problem is that when the circuit is put into use,the cable can heat up causing the sheath to become softer and the sharp edge can then cut thru to the copper.I was told that this was a code 2.Repairing decorations etc should not come in to it.On your inspection report you have to tell it the way it is.Repairing the deficiencies is a different kettle of fish.
 
I agree, however, i have seen many installations where they have not been used and they have all been ok, but i have seen some that are not, mainly due to three t&e's in a back box, which makes it more tricky to get the faceplate back, but i do understand what you are saying.

Another one of those fab grey areas that we all love.:D
 
I agree, however, i have seen many installations where they have not been used and they have all been ok, but i have seen some that are not, mainly due to three t&e's in a back box, which makes it more tricky to get the faceplate back, but i do understand what you are saying.

Another one of those fab grey areas that we all love.:D
:rolleyes:
Indeed. Maybe if the manufactors of metal back boxes gave us the option of a suitable 25mm oval knockout it would make things easier. Though I only use round conduit myself.
 

Reply to Missing grommets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

Replies
1
Views
1K
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
436

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top