Hi Ianpark.
The quickest answer to your question is this:
1) - Work out how many panels fit on the roof.
2) - Ditermine the Kwp of the system.
3) - Find out the Voc of the Panel @stc
4) - Mulitply all the panels by the Voc @ stc.
5) - example: Voc 45v @ stc x 8 panels = 360v
5) - Look at the input voltage of the inverter and check its within boundrys.
6) - But its more technical than that, then you need to check the voltage at -10d and at 25d 1250w radiance. and make sure the panels are still within the boundrys, this will ensure on the brightest coldest day of the year the system will fire up and on the hottest brightest days the system will still produce.
Im not an expert of those calcs thats why i use PV SOL to help me.
Remember - Add the voltage up to get in range of the DC input, and then add more strings in parrale, but not exceeding the maximum input current.
When adding more strings the voltage stays the same and its only the current (amps) that increases.
Visa versa, when adding panels in a string the current stays the same, but the voltage increases.
Hope this makes sense.
And please anyone else add to this or correct me if im not 100% correct.