we have a moeller z type overload through a contactor to a single phase motor, it is set to trip at 2.4a but doesnt! the motor is pulling 2.7a anyone any ideas why it isn't tripping
 
Took some searching, but here you go. All information taken from This Data Sheet.
[ElectriciansForums.net] moeller overload not tripping

Assuming you have one of these, Which has a trip curve of

[ElectriciansForums.net] moeller overload not tripping


Off the top of my head, the required trip time for a 20% overload on a motor to IEE standard curves is in the region of 50 secs or more. The set up you describe is 1.15 * set current and so will trip on 2 hours or more, perhaps not at all.

As benji says, you should series up the live feed from so that it loops between the left outgoing of the O/L back to the 2nd incoming of the contactor, then from the outgoing 2nd of the O/L back to the 3rd incoming of the contactor. Your outgoing live feed comes from the 3rd outgoing of the O/L. Neutral can either be switched through the 4th set of open contacts on the contactor or linked straight through unswitched.

That will force the O/L to treat it like a 3 phase supply and follow the 3 phase curve. Wire it as a straight L&N through only 2 sets on the contactor O/L set and you will follow the 2 phase curve, with a minimum trip time of ~25 seconds at 2*In.
 

Reply to moeller overload not tripping in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
920
Some year back there was a case of a young girl killed by being sucked down to the bottom of a pool when being emptied through the power drain...
Replies
23
Views
923
  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
Replies
15
Views
1K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
  • Question
Agree with Dave disconnect unused Phases on the outgoing side of the isolator. No reason to replace mcbs with single pole, unless you need room...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks