More than 1 circuit on mcb | on ElectriciansForums
Discuss More than 1 circuit on mcb in the UK Electrical Forum area at ElectriciansForums.net
Huddersfield
Hi, recently carried out an eicr at a rented property. There were 5x 1mm in a 6amp mcb for lighting.. my question is what code should I be looking at for this??
I am sure I have heard someone mention or read somewhere about overpopulating an mcb should be a code 2... but then i have also heard it’s all counted as 1x circuit so all the lights to the property are on 1x circuit.. which would be a code 3 recommendation they should be split.. advice would be welcomed.
cheers
If its fed from a single device it is one circuit. If in your professional opinion the conductors are adequately terminated and provided with fault and overload protection then no code is appropriate. There have been numerous debates here on the claims that 'multiple circuits' cannot be connected to a single device, ignoring the fact that it is multiple conductors forming one circuit, not multiple circuits. Nowhere do the regulations specifically prohibit this arrangement, nor do they require more than one lighting circuit in an installation.
A lighting circuit is a radial with several branches off whether from a switch or looped at the light. This one is just branched from the source.
why is it like this though? Is there shared neutrals where doubling up the circuits solved the problem, or is there another damaged 6A breaker that the circuit has been moved from as a “temporary” fix.
I’d say it’s 5 radial circuits and test at the extremity of each one....they will all be different lengths, different installation methods with branch’s etc giving different readings.....
It is ONE final circuit. A radial with five branches from the source. If there are no other issues, than it is perfectly satisfactory, and attracts no code at all.
It's also a circuit arrangement that makes fault finding easier.
Five.
You test at the extremity of each branch and record the highest, just like you would with a lighting circuit that leaves the CU on one cable, and then splits multiple ways.
Yeh 5 final circuits in 1x 6amp mcb. Looks like they have just added to the installation over the years, but instead of upgrading board for more ways, they have just put them all in 1.
There's absolutely no problem with that, as long as the circuit isn't overloaded. Used to be a maximum of 12 lamps for a 6A MCB, but this has become irrelevant with first cfl, and now LED lamps, although inrush still has to be considered.
I would make a comment, however, if this is the only lighting circuit.
Reply to More than 1 circuit on mcb in the UK Electrical Forum area at ElectriciansForums.net
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.