i'm wiring a final circuit for a 400v 7.5kw motor,15amp FLA
starting is DOL
i've calculated for the 30m final circuit using 4*4 swa a VD of 4v or 1%
i haven't calculated VD on the distribution circuit
would i be safe with 4*4 or should i calculate total installation VD to be sure
also is it standard practice to calculate using 100%fla or 125%fla
I would calculate total installation VD and 100% flc. Also need to check what type protection device is feeding that board in relation to your chosen type device for new circuit protection.Starting current may be a problem otherwise.
Reply to motor calc in the Electrician Talk | All Countries area at ElectriciansForums.net
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...