davelerave
how do you take into account starting current when sizing cables for 3-phase motors
in general thanks
in general thanks
Discuss motor calcs in the Electrician Talk | All Countries area at ElectriciansForums.net
I know nothing about motors, but i always thought it was the job of the motor starter to limit start up currents. Love to learn more on this subject though.
yes i know all that but thanks anyway
i'm enquiring about VD on startup or starting KVA -the voltage at the motor terminals on startup
Forget about VD at start up, you will end up running a cable 5 times bigger to compensate for it. Motors are designed to cope with it. So long as the cable can cope with the FLC +15% overload it will be OK. The MCB is there just to protect the cable and starter. But it has to handle the inrush current so a type C is in order, type D if it’s a biggish HE motor. The O/L’s in the starter will look after the motor.