Hi guys,

Could you clarify some thing for me?

If I've got an 1100w 230v motor running a pump, but don't know the power factor as its not listed on the rating plate, how can I work out overload rating?
 
What info is on the motor plate? Usually the FLC and power factor are on.
 
1.1kW on a motor plate means mechanical output power, not electrical input, so to calculate FLC you would need not only voltage and pf but also efficiency, which is not usually stated. But FLC is, Like Spoon I am surprised it is not on your motor unless your plate is completely missing. It will be around 9A for single-phase 230V depending on age and speed.
 
the rating plate has P1 as 1.1kw. there is no power factor and no efficiency rating listed. this is why I'm having problems. I've come across this before with the same pumps (Starite).

in the end I had to get the pump supplier to find out for me. seems daft that I can't work it out on site.
 
P1 is 1.1kW? That's confusing; 1.1kW is the standard motor size that replaced 1.5hp (output), but P1 is input power so it's a smaller motor than that and likely lower FLC than the 9A I suggested above. But it's eccentric for them not to state the FLC, the figure an installer most often wants to know along with voltage.
 
the rating plate has P1 as 1.1kw. there is no power factor and no efficiency rating listed. this is why I'm having problems. I've come across this before with the same pumps (Starite).

in the end I had to get the pump supplier to find out for me. seems daft that I can't work it out on site.
I'm also confused and wondering if they're correct saying the 1.1kW is actually P1.... I can't believe they could supply a motor with so little relevant info on the plate unless they're doing something shady like punting OEM stock to end users. I'd be on the phone or emailing the suppliers or agents for clarification unless there was a crystal clear and useful on-line spec sheet available.
 

Reply to motor call in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...
Replies
1
Views
183
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
381

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top