We are on a 600VAC delta system. There is this one motor that runs a saw arbour. The motor is 200hp, 1800 rpm, 189 FLC. We run the feeders through 400:5 CTs and the secondary on the CT's to a eutectic overload device which is set to 2.4 amps which should make the overload current value for the motor at 192 amps. This motor definately sees its share of overloading but for some reason does not trip any of the safety devices. I watched in a video recording that the motor had been stalled for approx 30 seconds after which it became a big ball of flame. During this time neither the fuses or the overload protection triggered a shut down. I did confirm the CT's are actually working and the overload control contacts are good also. I also inspected the motor after the fact and it showed signs of extreme overload but no signs of winding faults or shorts.
Does anyone have any ideas I can check as to why we might have not tripped anything on this type of fault.