R

rwacan

We are on a 600VAC delta system. There is this one motor that runs a saw arbour. The motor is 200hp, 1800 rpm, 189 FLC. We run the feeders through 400:5 CTs and the secondary on the CT's to a eutectic overload device which is set to 2.4 amps which should make the overload current value for the motor at 192 amps. This motor definately sees its share of overloading but for some reason does not trip any of the safety devices. I watched in a video recording that the motor had been stalled for approx 30 seconds after which it became a big ball of flame. During this time neither the fuses or the overload protection triggered a shut down. I did confirm the CT's are actually working and the overload control contacts are good also. I also inspected the motor after the fact and it showed signs of extreme overload but no signs of winding faults or shorts.

Does anyone have any ideas I can check as to why we might have not tripped anything on this type of fault.
 
Hi rwacan,
you could inject a current into the overload to see if it opens the contact within the correct time. These are thermal overloads and by there very nature are not very accurate, as a rule of thumb I apply a 20% accuracy to them. For this reason I always lean toward an electronic overload for protection of a motor of this size. If over time the overload has tripped out (possibly legitimately) there is always a temptation to increase the setting (if these are adjustable). As you can see if the setting was adjusted from 2.4A to 3.0A for instance the tripping current would have to be 240A to operate the overload. Because they are thermal devices a correction factor (temperature) is normally used Dependant on the specific application, the manufacturers website should have details of this and the relevant characteristic curves for the heater elements which are fitted in the eutectic overload.

Regards,

Dickylad.
 

Reply to Motor failure, Need help! in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
I always wanted to use a starter of this type around the house to operate some inconspicuous piece of equipment such as an extractor fan. Even...
    • Like
Replies
1
Views
2K
  • Question
I have a similar issue. In my case part of the problem is the cumulative residual current across different circuits protected by a single rod. I...
Replies
7
Views
2K
M
  • Question
What brand is the MCB you are using .... For a 1.5kw 230v DOL motor the recommended breakers are as follows... 32(b), 32(c) or a 20(D) This is...
Replies
13
Views
6K
M
cheers tony The cable fault finding was only part of the fun as it burnt out the bms interface tyco jelnet as well just for good measure We had...
Replies
2
Views
1K
maddfridge
M
S
31. When determining design current, the correction factor that is applied to a BS3036 rewirable fuse is a. 0.752 b. 0.527 c. 0.725 d. 1.725 32...
Replies
1
Views
2K
sxsparky
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks