At college I was ask to set the overload of a three-phase motor. I used P=V x I

Do you divide the motors wattage by 3 (as its three-phase) then divide by 230 or do you divide by 400?
 
The overload protection is always set slightly higher than the FLC of the associated motor usually in the region of 10 - 12%.

What figures did you have to work with???
 
You do need to do it for AM2, its in the booklet and was told on prep day. Tutor said you have to work it out by dividing the wattage by 3 and then dividing that by the voltage to find current.
 
When in DOL: Always set the motor overload to motor Full Load Amps, as stamped/etched on nameplate.

When in star-delta: overload over all then to motor FLA, overload in line side to motor only then 58% motor FLA

Never failed me in 16 years of machine control! Rather the overload trip than motor fail catastrophically. Nuisance tripping very unlikely unless motor rated too close to load. :rolleyes:
 
Last edited by a moderator:
im with silva fox on this one, set to FLA, or even better set to FLA and carry out running current test, then set slightly above your readings, ive never seen a serviceable motor run anywhere near the FLA on the nameplate in normal operation.
 
Back in the good old days you put 10 to 12 % on top. But not now. Modern overloads have this factor built in
and I agree with the efficiency
 
Just out of interest
The designers do a fancy calculation to calculate the fan or pump size, then add 10% (in case of error)
Thats why one of reasons you hardly see a motor doing its full duty
Unless there has been additions to the load
 
Can you use I = P/V to work out the FLA for a three phase motor if it isn't printed? If so, do you divide the power by 3 because its 3 phase?
 
i have got 0.63ohms written on my motor for the am2 and ive been told i need to work the overload setting out by a formula what do i do, i have to do it tomorrow
 
no its not, i was taught the same also. I was taught to measure current with clampmeter, and then set to 110% of that.


if you set according to FLA the windings should be protected


but the motor may be oversized and run well under FLA -so a lower setting could be used as long as nuisance is avoided
 

Reply to Motor Overload in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...
Replies
1
Views
97
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
306
  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
645
  • Question
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
Replies
1
Views
1K
Hi, Thanks for that, you learn something new almost every day! Regards Griffey
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks