speedtronic

A motor at our site was tripping on overload protection after 7-8 seconds when it was taken in service. When motor winding resistance was checked from phase to phase using multimeter, it was found that L1-L2 2.7 ohm L2-L3 2.7 ohm & L3-L1 5.7 ohm. What does it signifies & how it is effecting motor's operation & causing it to trip on over load?
 
Your overload tripping issue is more likely to be caused by another issue, but to be able to give you any direction i will need info:-
What is the motor doing (pump, drive etc)
Does it start up underload or off load if under load have you tried starting it off load
What is the rating of the motor and overload
What starting system is used D.O.L., star delta etc
Does the motor behave oddly when starting
Is there a gearing system in line

Just a few questions to get the ball rolling.
 
First check all connection on the block star point or delta link if all tight your motor has a shorted winding consult your nearest rewind shop for a rewind or replacement motor.(28 year working in industry tell me so) Good luck

just an other thought is the motor connection delta it could be open ciruit in one winding so your high reading is the other two winding in series yes I know 2.7 + 2.7 = 5.4 but it is close
 
Last edited by a moderator:
You could load check each phase to see what amps it was drawing. If its not drawing above the F.L.C that is on the rating plate and all your connections are tight on the motor/contactor/ and all terminals, and the pump or fan is not doing over duty i.e not offit curve then change the overload
 

Reply to Motor Overload in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
306
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
When working in the motor repairs industry you have to fill in test sheets and keep them for so long. Doing that will do is ok for most things but...
Replies
10
Views
3K
  • Question
I always wanted to use a starter of this type around the house to operate some inconspicuous piece of equipment such as an extractor fan. Even...
    • Like
Replies
1
Views
2K
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks