Motors over 0.375kw | on ElectriciansForums
Discuss Motors over 0.375kw in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Am I right in thinking I saw a regulation that was that any motor over 0.375 kw had to be on a DOL starter?
I would suggest it needs overload protection, this can be achieved via a starter and very common practice, however I would like a bit more info from you so we can advise what's required, what size motor? what's it doing?
I'm an industrial apprentice so I do know about the overloads! :D I was Litterally thinking this at work, swear I saw a regulation about needing a starter! Must have been that it needed overload protection! Thank you guys! A friend was talking to me about that he had a 3hp or 2hp motor on a compressor made my memory jog!
The regulation you seek is 552.1.2
Motors over 0.37kw need to be provided with control equipment incorporating a means of protecting against overload.
Also compliance with section 537.5.4 is needed too.
Reply to Motors over 0.375kw in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
That sounds to be more of a control issue rather that a motor issue Are all the limit switches working properly and not sticking occassionally
Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...