Moving CU from one side of wall to other side of wall - Safe zones?? | on ElectriciansForums

Discuss Moving CU from one side of wall to other side of wall - Safe zones?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

leo79

-
Joined
Jul 12, 2009
Messages
74
Reaction score
53
Location
1
Hi

Basically, I've just finished the 1st fix on a property, customer and builder wanted CU to go into kitchen cupboard where the gas meter was. Gas meter has been disconnected, builder waiting on National Grid to come and re-site gas meter externally.

National Grid came out on Friday, customer has been informed off the cost, ÂŁ700-ÂŁ800, which is the price I thought it would have been, I've never known it to be less than ÂŁ500. Customer not happy with price and wants CU moved, god knows what price she had in mind!

I'll be charging extra to move it so I'm not trying to get out of carrying out the extra work, but we're limited to where it can go.

My suggestion would be to go back to back to where it was originally going which will take it into the WC off the hall.

Now I realise that the regs state that a safe zone is extended to the reverse side of a wall for an accessory/switchgear,where the wall is 100mm thickness or less, but the wall is single brick with render, plaster and tiles, making around 120mm.

Common sense would tell you that the location of the CU would mean that all cables would be run on the reverse side of the wall as there is nowhere else they could be run.

Any thoughts?

Thanks

Leo
 
Last edited:
Go ahead and do it.
sometimes the practicalities over-rule the guidelines.
no-ones gonna be measuring the thickness of the wall when the jobs finished lol.
lifes too short :)

Just get builder to box it in with small cupboard when wiring is completed.
 
Last edited by a moderator:
if you want to be doubly certain you could flush fit a 2-3mm steel plate over the cables.
 
What he said ^^^^
 
just thinking!!!
if you put DB in wc and your cables drop down on otherside of wall in the kitchen, are the kitchen cuboards going over the finished wall of your cable drop.
 
Why don't you pull the cables back up to the floor cavity and drop them down to the CU direct?

Or at least pull them back up to within 150mm of the ceiling and pass them through the wall within the safe zone?
 
just thinking!!!
if you put DB in wc and your cables drop down on otherside of wall in the kitchen, are the kitchen cuboards going over the finished wall of your cable drop.

Yes, cables are in situ. Kitchen cupboard was going over CU but gas meter will be going in there now.

Why don't you pull the cables back up to the floor cavity and drop them down to the CU direct?

Or at least pull them back up to within 150mm of the ceiling and pass them through the wall within the safe zone?

Not possible due to layout of stairs, WC is under stairs, stairs have winders at top and 2 levels.

Cables will be coming through the wall within safe zone of WC as this would be going ceiling height anyway, but ceiling height in WC is much lower than ceiling height of kitchen.

Question!!! where do you intend to have this steel plate installed?? over your cable drops?

Erm........possibly?
 
ok mr stupid comes along drills through from wc into kitchen to get above them kitchen units straight through your cables your steel plate is doing nothing.
 
also you have to install the steel plate to satisfy the regs, the builder will say hes done it but really he couldnt be bothered and thinks it wont matter
 
ok mr stupid comes along drills through from wc into kitchen to get above them kitchen units straight through your cables your steel plate is doing nothing.
No.... CU is ceiling height in WC. cables are through wall and up. ... at least that's how i read it....
 
ok mr stupid comes along drills through from wc into kitchen to get above them kitchen units straight through your cables your steel plate is doing nothing.

It would be impossible to drill through from WC to above kitchen units.

also you have to install the steel plate to satisfy the regs, the builder will say hes done it but really he couldnt be bothered and thinks it wont matter

Is a steel plate a requirement of the regs?
I would never take anybody's word that they were going to do something.

No.... CU is ceiling height in WC. cables are through wall and up. ... at least that's how i read it....

Correct.

different ceiling heights

Whats your point?
 
ok mr stupid comes along drills through from wc into kitchen to get above them kitchen units straight through your cables your steel plate is doing nothing.

Mr stupid would probably drill through cables whether they were in safe zones or not.
And if we keep coming up with " what if " scenarios nothing would get done would it ?
 

Reply to Moving CU from one side of wall to other side of wall - Safe zones?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
884
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top