M
martinh287
Hi guys just wanting to confirm I am right in my thinking when carrying out EICR on multiple distribution circuits within a three phase board it is my responsibility to carry out the report up til the clients db only. When dead testing I only have a limited timescale for every circuit to be off usually 5 min for all rcd tests IR test and R1+r2 on mains cable. So that's the mains sorted I then when time permits would switch off all clients db boards and test the full 3 phase board at 500v and any dodgy results further investigated.
The reason for this thread is to find out before I do it in the real world is could I test l+n to earth at 250v with the clients db main switch (30ma rcd) closed and any ad normal results further tested or will I get strange results testing through the rcd
Sorry for been long winded
The reason for this thread is to find out before I do it in the real world is could I test l+n to earth at 250v with the clients db main switch (30ma rcd) closed and any ad normal results further tested or will I get strange results testing through the rcd
Sorry for been long winded