Hi All,
I have been asked to wire some lighting for an office and corridor involving sensor operation and Lighting distribution units and I was wondering what the best way of achieving this would be??

Briefly I will have 7 600x600 Grid lights in a corridor that will be operated by 3 sensors - when any of the sensors is activated the lights will operate. some of the lights will also be emergency lights.
 
Thanks for the replies - so lets see if I've got this right??
Assuming that the load for the lighting is greater than the sensor loading. I could run a circuit out to the sensors and just parallel the sensors together on the circuit (L/N/E & S/L) and bring the S/L back to the contactor. Feed the lights from the contactor.

Do I need a separate breaker to feed the sensors and the lights via the contactor as the protection for the sensors will be less than for the lights??
 
you select the protection device/s according to the load/s and the cable/s feeding the load/s. so if using a contactor, you might have a B6 for the sensors and a C10 or C16 for loads. you could even split the loads over 3 poles of a contactor.
 
Also may be easier to mount 6A mcb in enclosure with contactor - that way one feed, the 16A or whatever, can do both (only 1 way required at DB)

When you calc load don't forget multiplier (assuming standard fluorescents)
 
Last edited by a moderator:
What traffic is there? .... if they will be switching a lot then fluorescent modulars will see a shortened lamp life especially if switch start...

Id be inclined to estimate the switching duty before choosing this method and/or choose an appropriate fitting like LED mods to give good service life.

Id wouldn't personally be switch the fittings through the PIR's even if they are within the PIR's switching capacity - PIR's are prone to failure of switching contacts and especially with accumulative inrush which is hard to calculate - a contactor is the best way ahead.
 
I wouldn't bother with a contactor for 7No 600x600 modular fittings.
Just use a recessed crabtree master & slave motion sensor… hard wire the master & plug in upto 5No slave sensors. I believe these will switch quite happily up to 1100watts of hf fluros, unlike the paltry 500watts of stand alone PIRs.
 

Reply to Multiple sensors for internal lighting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

  • Question
Well conventional wisdom says that you just parallel ('piggy back') as many switch sources as you need, all fed to the contactor coil. If for...
Replies
4
Views
981
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top