Evening all,

Could some bright spark clarify something for me please.

In the OSG Table I1 Pg182 (Green) the values of resistance/metre or (R1+R2)/metre for copper and aluminium conductors assumes a value of 20 degrees as the ambient temperature.
Lets say a properties ambient temperature is 25 degrees I need to add in a multiplying factor from Table I2 Pg183. (I get this bit)

My question is, Is it assumed that the original temperature of 20 degrees stays as is, and you add an additional 5 degrees [correction factor 0.94] or,
add the multiplier for the expected 25 degrees [correction factor 1.02]

Your help as ever is appreciated
 
Thanks for your reply. I'm aware you mutiply it. My question was particular to the correct choice of correction factor. So in Table I1 there is the asumption that ambient temperature of 20 degrees. If the ambient temperature is in fact 25 degrees do I a) add a 5 degree correction factor in effect making it up to 25 degrees or b) use the 25 degree correction factor.

Thank you in advance
 

Reply to Multiplers - ambient temperatures in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
933

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top