....am now bored stupid but still not fit for work, with that in mind I’m going to use the time and sort out a few bits in doors,starting with this...
TN-s supply to meter into 100a-100ma s type rcd then into 25mm swa and into the CU under the stairs about 5/6 mtrs away under upstairs floor through joists ( I strengthened the joists when I moved in as I was not happy with a cable that size going through!....I want to change the rcd for a 100a dp isolator for discrimination purposes but with the installation method of the swa (under floor boards) i’m concerned with protection should someone ever hit the cable? Not likely I know but.....Or am I over thinking as it’s armoured? Cable sheath not earthed either....this was installed before my time and before I had any interest in electrical work.
TN-s supply to meter into 100a-100ma s type rcd then into 25mm swa and into the CU under the stairs about 5/6 mtrs away under upstairs floor through joists ( I strengthened the joists when I moved in as I was not happy with a cable that size going through!....I want to change the rcd for a 100a dp isolator for discrimination purposes but with the installation method of the swa (under floor boards) i’m concerned with protection should someone ever hit the cable? Not likely I know but.....Or am I over thinking as it’s armoured? Cable sheath not earthed either....this was installed before my time and before I had any interest in electrical work.