Wired two RCD sockets on a radial today next to a sub-DB in a large factory unit. The new circuit was connected to an existing redundant 20a MCB which had served a control item which I'd disconnected a while back. Now based on the possibly iffy logic that because the protective device was already in place I decided that I'd get away with a MW because I wasn't adding anything to the existing DB.
Truth is I just couldnt be assed to gather the plethora of information required for an EIC to be correctly filled in for such a p***yass job.
A MW seemed more than adequate...Preparing now for a right good telling off.
 
My view is that Westward is correct in that it's a new circuit and requires a eic if you go by the book.
But I'd probally do as Wirepuller did and issue a mwc for this job, the mcb was already in place and if it supplied a socket already there and you extended it to the 2 new sockets there'd be no discussion, a mwc would be issued.
 
In his words New circuit :D
My view is that Westward is correct in that it's a new circuit and requires a eic if you go by the book.
But I'd probally do as Wirepuller did and issue a mwc for this job, the mcb was already in place and if it supplied a socket already there and you extended it to the 2 new sockets there'd be no discussion, a mwc would be issued.
That was my first thought Andy it's got to be an EIC , a contentious issue.
 
Just do what most people do and write the results in pen on the wall adjacent to the DB.
You know ze 0.12 etc etc. :rolleyes:

Tho in all seriousness the trauma of trying to take a ze to a functioning installation just because a couple of sockets have been added.
 
Thanks for the input chaps, I think technically an EIC would be the correct thing. The MCB was in place, the previous circuit connected to it had been disconnected, but nevertheless I connected a new and completely different circuit to it.
But I suspect I'll be trying to justify a MW for this sort of thing more and more in the future. As Dave OCD says, the time and effort an EIC now involves is a sledgehammer to crack a nut for this sort of thing. It's really designed for major works or new installations. Whenever I'm faced with compiling an EIC I cant help thinking we need something intermediate between a MW and EIC, say for a maximum of 1 new circuit. I confess in the past I have extended or spurred from existing circuits just to avoid an EIC when compiling one would be a pain, such as in commercial/government premises where access to the required areas is nigh on impossible without a major faf.
 
In a perfect world you could easily get your hands on the most recent EICR and then copy all of the info over such as Ze and the tick boxes to your EIC. Then you'd only have to perform the same tests as you would with a minor works

Not sure I agree with that ..............I may consider this route IF I had done the EICR ......... but use somebody else's figures ........... no
 
I do plenty of small installs in a factory where I did an EICR in 2016. Plenty dis boards so I just do a zs at board in question and cert to suit.
Similar to WP, today used an swa, which used to feed a portacabin, for a small compressor in a new quick build...so it ticked the right boxes.
Trouble is, I don't want to start ticking another load of boxes, either....pain in the butt. :(
 
In a perfect world you could easily get your hands on the most recent EICR and then copy all of the info over such as Ze and the tick boxes to your EIC. Then you'd only have to perform the same tests as you would with a minor works
Thats assuming the eicr is worth the paper it is printed on and has not been done by a drive by cowboy in his bodge job van.
all well until you copy the results from such an eicr and they are made up when really the place is a death trap...
 
Another problem I find is with ind/com kitchen work, maybe in schools or shopping centres. They may be small jobs, such as gas cut out panel supplies. It's virtually impossible to get any supply info or access. In such cases it has to be a case of noting on the cert.
Imagine trying to get info or access at Manchester airport or Liverpool Echo arena. It's impossible....and, sometimes, your dealing with awkward sods who don't want to know.
 
If it's not practical to carry out a Ze test I would rather put the Ze from the current EICR and leave a note on the EIC than leave the box blank.

I asked this question to my NICEIC assessor and he said that it is acceptable as long as the EICR certificate number is stated in the notes on the EIC.

Obviously not ideal but better than LIM
 
I would agree that an EIC would be technically correct (just).
However if you considered the job as a long period job, you came in removed the old cable and replaced it with a new cable and also removed the old accessories on the end of circuit and put new ones in, still the same old circuit just with a new cable and accessories!
If the job had been done in stages each one would have been a minor works.
 
... you came in removed the old cable and replaced it with a new cable and also removed the old accessories on the end of circuit and put new ones in, still the same old circuit just with a new cable and accessories! If the job had been done in stages each one would have been a minor works.
For some reason reminded me of this classic :)
 
For this situation there should a cert for when you are just installing one or two circuits as others as said its not always posible to access the main incoming supply of large installations , You can not put LIM on a eir so what do you do ?fill the report with N/As .
 
For this situation there should a cert for when you are just installing one or two circuits as others as said its not always posible to access the main incoming supply of large installations , You can not put LIM on a eir so what do you do ?fill the report with N/As .
Depends if that means 'Non Applicable' or 'No Access'. ;)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
MW or EIC?...........
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Deleted member 9648,
Last reply from
Flanders,
Replies
26
Views
3,208

Advert

Back
Top