Evening chaps,

A little help with what i think is a grey area. Im going to install a twin socket from the DB off the 32a ring RCBO. Does this class as an alteration where i will issue a MWC or does it warrant a EIC?

Thanks
 
Minor Works Certificate, as its just an addition to an existing circuit and doesn't extend to the provision of a new circuit.

Source: Appendix 6 BS7671.

Edit, just re-read your post, do you mean take the cable for the socket and place it directly into the RCBO / CCU?
 

Reply to MWC or EIC? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
599
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top