MWC - Required or not - LED Light fittings | on ElectriciansForums
Discuss MWC - Required or not - LED Light fittings in the Commercial Electrical Advice area at ElectriciansForums.net
West Yorkshire
I've recently upgraded some light fittings that are probably 15-20 years old in an industrial unit to LED fittings
  • 150W Low bay LED's internally
  • 80w LED light fittings with separate photo-cells on external lighting column opposite warehouse.
Is there a requirement to issue a MWC
If you decide not to, though I would be inclined to due to testing, you could add test results to invoice so that it is recorded. MWCs are usually quick to produce and carry the results in appropriate boxes.
I would consider changing current using equipment an alteration to a circuit and issue a MWC.
It’s not required by BS7671.
Would probably help to tick some boxes under CDM Regulations.
Could make a mention in the invoice about ‘tests conducted to verify suitability of circuit/installation for replacement of fittings’.
Reply to MWC - Required or not - LED Light fittings in the Commercial Electrical Advice area at ElectriciansForums.net
For my hapeneth and learnt from hard recent experience, the term LED transformer and driver tend to be used interchangeably, when they are...
Thanks for the input guys. Lighting track is out of the question. The routing (h section guirders and angle iron) means that swa cable clipped...