My EICR test guy says I need to change my bathroom ceiling light to an IP65 rated. Research says I need an IP44. The lamp is about 2.45m above the floor and about 30cms outside the side of the bath. Has he made a mistake or have I?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss My EICR test guy says I need to change my bathroom ceiling light to an IP65 rated. in the UK Electrical Forum area at ElectriciansForums.net
OK, I will try to get photo posted. It's just a standard light fitting which I've never had problems with as it is away from any water source.As with a lot of these types of post a picture or two would help
The light is nowhere near any source of water. My confusion is why he said the fitting must be IP65, not IP44 (or IPX4) as in the regs. I'll try to post a photo.This is really up to the inspector to decide.
Although technically outside any of the zones, being above 2.25m from the floor, (and therefore not required to comply with zoning regulations) the light still has to be suitable for the environment it is installed in.
If the light was in zone 2, then the MINIMUM applicable IP rating would be IPX4. If it was possibly subject to splashing of water from a shower head, then the minimum would be IPX5.
I sometimes come across metallic fittings that are not in any zone but are corroded. In this case I might C3 them, as they are clearly unsuitable for their environment.So if the standard light fitting is probably only IP 20 and above 2.25M of Zone 2, then how would you code it, & maybe it is RCD protected as well?
Reply to My EICR test guy says I need to change my bathroom ceiling light to an IP65 rated. in the UK Electrical Forum area at ElectriciansForums.net