My EICR test guy says I need to change my bathroom ceiling light to an IP65 rated. Research says I need an IP44. The lamp is about 2.45m above the floor and about 30cms outside the side of the bath. Has he made a mistake or have I?
 
This is really up to the inspector to decide.

Although technically outside any of the zones, being above 2.25m from the floor, (and therefore not required to comply with zoning regulations) the light still has to be suitable for the environment it is installed in.

If the light was in zone 2, then the MINIMUM applicable IP rating would be IPX4. If it was possibly subject to splashing of water from a shower head, then the minimum would be IPX5.
 
This is really up to the inspector to decide.

Although technically outside any of the zones, being above 2.25m from the floor, (and therefore not required to comply with zoning regulations) the light still has to be suitable for the environment it is installed in.

If the light was in zone 2, then the MINIMUM applicable IP rating would be IPX4. If it was possibly subject to splashing of water from a shower head, then the minimum would be IPX5.
The light is nowhere near any source of water. My confusion is why he said the fitting must be IP65, not IP44 (or IPX4) as in the regs. I'll try to post a photo.
 
Here is a photo of my bathroom light fitting.
[ElectriciansForums.net] My EICR test guy says I need to change my bathroom ceiling light to an IP65 rated.
 
Last edited by a moderator:
So if the standard light fitting is probably only IP 20 and above 2.25M of Zone 2, then how would you code it, & maybe it is RCD protected as well?
I sometimes come across metallic fittings that are not in any zone but are corroded. In this case I might C3 them, as they are clearly unsuitable for their environment.

In some cases I might choose not to allocate a code, but add a comment in the report that, in my expert opinion, the light is not suitable and should really be changed.
 

Reply to My EICR test guy says I need to change my bathroom ceiling light to an IP65 rated. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
ok cheers for the help lads
Replies
7
Views
711
SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top