Hi guys
need a little guidance on a install I got to do this week
we got a bungalow on a 3phase supply with 3phase cu
The kit we have is as follows
3 x inverters 3.6 growatts
1x 3 phase meter

i was thinking of taking a 3 phase supply to workshop Not far so thinking of 6mm swa
on a 3p mcb 16amp
to a 3ph cu then out from 16 amp mcb 3 pole to 3 phase isolator 20 amp to meter then to the inverters

any help on this would be great as its my first 3 phase install
cheers JonJon
 
Hi guys
need a little guidance on a install I got to do this week
we got a bungalow on a 3phase supply with 3phase cu
The kit we have is as follows
3 x inverters 3.6 growatts
1x 3 phase meter

i was thinking of taking a 3 phase supply to workshop Not far so thinking of 6mm swa
on a 3p mcb 16amp
to a 3ph cu then out from 16 amp mcb 3 pole to 3 phase isolator 20 amp to meter then to the inverters

any help on this would be great as its my first 3 phase install
cheers JonJon

What's a growatt when it's at home?
 
Is it ok to go from main 3phase house cu on 16amp 3 pole mcb to a
20 amp three pole & neutral isolator into meter. Then out to inverters
?...
 
I'd want to use a separate MCB for each phase / inverter, and separate single phase isolator per inverter.

so 16A 3 phase MCB >>> 3 phase meter >>> 4 pole isolator >>> 4 core and earth >>> distro board with 3 x single phase 16A MCB >>> single phase isolators x 3 >>> inverters x 3

or similar.
 
Thanks Gavin
so go down the cu route
can I ask why you put the meter & 4pole isolator before the sub 3phase board cheers Jon

16amp 3pole mcb --- swa --- adapt box--- meter-- 4pole iso --- 3phase cu 3 way --- 16amp mcbx3 --- 20amp isolatorsx3--- inverters
 
Thanks Gavin
so go down the cu route
can I ask why you put the meter & 4pole isolator before the sub 3phase board cheers Jon

16amp 3pole mcb --- swa --- adapt box--- meter-- 4pole iso --- 3phase cu 3 way --- 16amp mcbx3 --- 20amp isolatorsx3--- inverters

So that the meter is monitoring the whole sub board I imagine.
 
so what then happens when customer uses the spare ways on board for something else
wouldnt it be better just to meter from the cu to inverters ??

cheers jon
 
or similar.
this bit should answer your question, you're the system designer, you design it, but usually the meter would go near the main board - not always though, so design it how you think best suits the situation.

re the 2nd distro board, use a 3 way with single phase MCBs for each phase, and common neutral bar - the incoming cable is already protected at the main board, then you'd have no spare ways to worry about. Either that or label it up for solar only, if anyone ignores that in the future, then that's their look out, can't really legislate for idiots ignoring specific instructions.
 
or similar.
this bit should answer your question, you're the system designer, you design it, but usually the meter would go near the main board - not always though, so design it how you think best suits the situation.

re the 2nd distro board, use a 3 way with single phase MCBs for each phase, and common neutral bar - the incoming cable is already protected at the main board, then you'd have no spare ways to worry about. Either that or label it up for solar only, if anyone ignores that in the future, then that's their look out, can't really legislate for idiots ignoring specific instructions.

You need to include 25% spare capacity. Is that not in the regs somewhere? Can't be bothered to look at the mo but sure it was a reg that any new install shall have spare capacity.
 
Hi ATM84 , I have not fully read this thread so apologise if I have the wrong end of the stick , so to speak !?
I think Gavin is suggesting that all the inverters are first fed in to a sub board and then back ? If so I would personally say it was bad practice to deliberately plan to leave spare ways ( possible parasitic loads ) , as it is only really being used to consolidate all of the inverter feeds into one for metering and possibly connecting a g59 protection relay .
 
Hi ATM84 , I have not fully read this thread so apologise if I have the wrong end of the stick , so to speak !?
I think Gavin is suggesting that all the inverters are first fed in to a sub board and then back ? If so I would personally say it was bad practice to deliberately plan to leave spare ways ( possible parasitic loads ) , as it is only really being used to consolidate all of the inverter feeds into one for metering and possibly connecting a g59 protection relay .

Thanks for your reply. Its good there are some ppl on here willing to help others and explain things.
 
You need to include 25% spare capacity. Is that not in the regs somewhere? Can't be bothered to look at the mo but sure it was a reg that any new install shall have spare capacity.
this isn't a sub board for use by anyone else for anything else, it'd be generation specific, and only allowed for use with that metered system if installed with the meter at the other end of the cable. Same principle as a FCU, just splitting down to 3 separate phases.

If there is likely to be a demand to use the cable / sub board for other purposes then the generation meter would need to be moved to the other side of the sub board, then you can leave as many spare ways as you want.
 

Reply to My first 3 phase solar pv systems need help in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

If the batteries are charged and the house is taking little then the full production of the panels will be dumped into the grid. As you have set...
Replies
1
Views
477
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
656
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
  • Question
For anyone looking into the same thing I’ve just found a guy who did an experiment to see if this is how the 3 Phase meters counted units and it...
Replies
3
Views
1K
  • Question
We use one from Stephill generators, it covers the while check / switch / return sequence and included a charger to keep the generator's battery...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks