short story, I've come across a 3 phase distribution circuit wired in 4mm singles on 63a hrc fuses. I found this because 1 of the phases was on a 20a and had blown. this seams wrong to me but as I said I don't have much ind experience. this is a new circuit from a tap off box. also I don't want to drop someone in the rubbish if it is wrong.
 
So one phase was 20A and the others 63A? If they are pvc singles contained in conduit they are only rated at 28A. If they are thermosetting (BS7211) they are rated at 44A.
 
Who would you be dropping in the crap that so concerns you and why do you priorities this against both public and property safety?

My next concern is you are getting involved with situations you have little to no experience in, it may be the fact that overload protection of the cables is not afforded due to an exemption found in the BS7671 regarding fixed load equipment, this could be what you have come across although it's also common to find bodged work and poor design so with knowing all the details of electrical install and the load itself it's hard to call on whether it complies or not and if it's a hazard.
 
the person I don't want to drop in it, is who ever connected the 4mm to the 63a fuse. the omission of overload protection was what I was thinking of but as a distribution circuit I can't see how that would apply (my lack of experience). the 3 lives have been clamped and read 17, 15 and 26a respectively. this is not my problem to fix but I feel I should raise my concerns if they are justified.
 
What is it supplying, it is not just overcurrent protection but the issue of the conductors withstanding fault current.
 
Those conductors are undersized, with a dist board there is no way of knowing any future loading, but if alterations/additions are carried out hopefully a competent person SHOULD see the situation. Theoretically there is a possibility that with any future loading those conductors could seriously be overloaded.
 

Reply to my industrial inexperience? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695
  • Question
Thanks for the input guys. Lighting track is out of the question. The routing (h section guirders and angle iron) means that swa cable clipped...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top