Hi all,
After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone.

Customer wants to upgrade from rewirable CU to RCBO so fairly old wiring but no signs of cable breakdown or anything totally messy on inspection. This circuit basically holds everything inc. boiler etc but exc. lights and cooker.
Ring continuity tests are slightly messy but well within limits.

IR testing L/N & L/E = approx 150M, however N/E = dead short @ 0M

Unplugged everything, isolated all FCUs that I can find but still no luck. Temporarily tried the circuit on a RCD to check I hadn’t missed any loads or just being an idiot but it only holds for a minute or two before it trips confirming a fault.

My thoughts are to now break down the legs of the ring and go hunting the fault similar to finding a continuity fault.

Any one have any other options or go to places to start that might speed up the process??

Cheers in advance.
 
Were all the ring conductors disconnected when you did the IR test? (I know the CPCs should technically be left connected during this test, but we're talking fault finding here).

Out of interest, what does it read if you test using the low Ohms range of your tester?
 
Is there an immersion heater?
Also, checking an obvious question, you had the Neutral's disconnected at the CU when you did the test showing 0 N-E ?
(just double checking you aren't measuring the TNCS link, or indeed another circuit could have the fault)

Otherwise - yes - break ring somewhere and see which half it's on.
 
Sounds like it's going to need the ring circuit splitting.

I'd still test it on the low Ohms range though to see what actual resistance you are talking about here. Remember the MR range will show 0R but it probably won't actually be that.
 
As @DPG says, if it can be detected on a low resistance continuity test it might speed things up. Leaving the CU ends disconnected and measuring at each socket until you find the two lowest L-E readings. In theory it's between them if neither of them are spurs.

Best of luck. You'll get there in the end. If you reach an understanding of the problem in under 2 hours you'll have done well!
 
If it's a conventional ring just make an educated guess where the mid point is and split it there, and test each leg from the CU. That should rule out half the ring. Split the faulty leg at its mid point, test again. Keep going till you run out of places to split it and you will have hopefully found the fault, or at least be close. It's the most efficient way, known in other fields as a "binary search".

If on the other hand it's a DIY disaster zone like the one I had last week, which was a figure of 8 bodge with spurs off spurs off spurs you're in for hours of fun. Eventually traced it to a choc block plastered into a (now slightly damp) wall.
 

Reply to N/E fault IR=0 - RCD won’t hold in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top