Hi,
I am curious, could someone please explain how a N-E fault confined to the non RCD side of a board could trip the RCD, given that N-E is joined at the TX, or cutout...
 
N-E faults can cause some weird effects. i had one where a N-E fault on 1 side of a new dual RCD CU stopped both RCDs from tripping, even with the test buttons, but when a load was applied to either side, both RCDs tripped.
 
Richard Burns drew a good diagram once that 'I think' showed how this would be possible but I cant find it. I cant understand how it can happen though (from a N-E fault) as the only connection between the non RCD side and RCD side is from the supply L and N in the top of the RCD, so even if there is a current imbalance on the non-RCD side how can this impact on the RCD as none of the current has been flowing through the RCD?
 
Last edited:
N-E faults can cause some weird effects. i had one where a N-E fault on 1 side of a new dual RCD CU stopped both RCDs from tripping, even with the test buttons, but when a load was applied to either side, both RCDs tripped.
Out of interest, did you have a short N-E or low insulation resistance N-E when you had this?
 
No, not possible, unless there is also a fault on the RCD side.
Current will flow along any and all available paths.
RCDs operate by detecting imbalances between Line and Neutral.
A N-E fault on the RCD side, will cause some of the current which would flow along the Neutral conductor, to flow along the Earth conductor. bypassing the RCD.
As such the RCD will detect that there is more current flowing along the Line conductor, than along the Neutral conductor, and operate.
An N-E fault anywhere else cannot affect the amount of current flowing along the Line and Neutral conductors attached to the RCD.
 
Yep,the "connection" between differing sides of such a board,may be due to other,"off-board" reasons. The tripping being just the start of that illuminating journey :icon12:
 

Reply to N-e fault on non RCD side of db tripping RCD??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
763
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top