Hi guys,

I fitted a new CU last week. After IR testing I found a dead short 0 on N & E. advised the customer this would need to be sorted before installation as New CU will have a sexy little device called an RCD which will keep tripping when he turns lights on and off or plugs stuff into the ring main. When he asked me why? I told them that there would be an imbalance that the rcd will react to etc.. etc... But when asked about how the light switches might make the rcd trip as they weren't on the rcd I bundled through the explanation which seem to satisfy them but to be honest I would like to have the science of this explained to me just to make sure I have it correct in my head. Bit apprehensive about posting here again. I am pretty new to the industry and after a terminology slip up a week or so ago (been talking class two lights with a customer all day and referred to a plastic socket as class two, yeah I know! Nob ed!) I got a load of Micky taking etc... Nothing wrong with banter and I'm a big boy now ha ha but not very helpful when you need to get an answer. So please any help will be greatly appreciated as will any Micky taking as long as its in that order ha ha.

Thanks
 
The lights should also be on the RCD, as for the dead short reading... Did you look into it? We're all loads unplugged from the ring that you tested etc?
 
Hi guys sorry bad description on my part. The board is split load all circuits are on rcd what I should have said is not the rcd that cover the ring whee the fault is. I cleared the fault. My method was

1. Unplug everything and IR test again found same fault.
2. Broke ring in middle tested both ways.
3. Repeat step 2 until I found the fault.

It turned out to be a exposed N touch metal babackbox my Q is

what is the science that allows a light switch covered by a different RCD to trip the other rcd that covers the ring where the fault is.


ta guys
 
what is the science that allows a light switch covered by a different RCD to trip the other rcd that covers the ring where the fault is.



usual cause of that is a borrowed neutral or a neutral cable inserted into the wrong N bar.

 
I had another job. All neutrals were correctly connected, no borrowed neutrals with an N to E fault on the ring circuit. When switching lights on or off sometimes it tripped the rcd that covered the ring not the rcd that the lights. How would that happen does the sudden on or off of the lights cause a small surge or something in all other circuits that due to the N to E fault cause the other rcd covering the ring to trip? I ask this because after clearing that fault the rcd hasn't tripped since.
 

Reply to N E fault on ring. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
93
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
889
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
455
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
801

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top