I'm starting a new construction single-family residence, I know with the 2020 NEC they require an emergency disconnect on the exterior of the home. My confusion is do I treat the emergency disconnect as the main disconnect, and the main breaker panel would be wired like a subpanel with separate ground and neutral bars?

For example the service two hots and neutral into emergency disconnect, connections made and service entrance cable ran through wall to main panel. The question is on the emergency disconnect do I bond the neutral bar to the enclosure and attach the ground electrode wire to the bonded bar? Then the main panel indoors would be treated with separate ground and neutral bars, like a subpanel? The ground between the indoor main panel, and outdoor emergency disconnect would then be bonded at the underground electrode connection. Let me know if this is confusing and I can sketch what I'm referring to, or if someone has a typical diagram with the emergency disconnect that would be helpful. Thank you
 
I'm starting a new construction single-family residence, I know with the 2020 NEC they require an emergency disconnect on the exterior of the home. My confusion is do I treat the emergency disconnect as the main disconnect, and the main breaker panel would be wired like a subpanel with separate ground and neutral bars?

For example the service two hots and neutral into emergency disconnect, connections made and service entrance cable ran through wall to main panel. The question is on the emergency disconnect do I bond the neutral bar to the enclosure and attach the ground electrode wire to the bonded bar? Then the main panel indoors would be treated with separate ground and neutral bars, like a subpanel? The ground between the indoor main panel, and outdoor emergency disconnect would then be bonded at the underground electrode connection. Let me know if this is confusing and I can sketch what I'm referring to, or if someone has a typical diagram with the emergency disconnect that would be helpful. Thank you
I can't claim to know the code but think about the intended purpose of the Emergency Disconnect; To remove ALL sources of power from the installation and so it would be prudent to treat as the MAIN disconnect.

If you have multiple sources of power; public utility, private generator, solar, then you'll want to ensure these also go through this disconnect so that 1 operation kills everything.

@Megawatt may be able to better advise.
 
If you have multiple sources of power; public utility, private generator, solar, then you'll want to ensure these also go through this disconnect so that 1 operation kills everything.
The supply disconnector mentioned here might be something akin to our cut-out so it is purely for the mains coming in just after the billing meter.

I agree though if they have backup power from generator/solar+battery/etc then having a single means of safe disconnection for everything further down from change-over switches is a very good idea.
@Megawatt may be able to better advise.
Definitely!
 
Let me know if this is confusing and I can sketch what I'm referring to, or if someone has a typical diagram with the emergency disconnect that would be helpful. Thank you
That might be helpful.

Many of the folks on here are UK-based so very different rules to the NEC, but we still see what is going on over the pond as interesting.
 
I'm starting a new construction single-family residence, I know with the 2020 NEC they require an emergency disconnect on the exterior of the home. My confusion is do I treat the emergency disconnect as the main disconnect, and the main breaker panel would be wired like a subpanel with separate ground and neutral bars?

For example the service two hots and neutral into emergency disconnect, connections made and service entrance cable ran through wall to main panel. The question is on the emergency disconnect do I bond the neutral bar to the enclosure and attach the ground electrode wire to the bonded bar? Then the main panel indoors would be treated with separate ground and neutral bars, like a subpanel? The ground between the indoor main panel, and outdoor emergency disconnect would then be bonded at the underground electrode connection. Let me know if this is confusing and I can sketch what I'm referring to, or if someone has a typical diagram with the emergency disconnect that would be helpful. Thank you
By definition of the NEC says that the first panel or disconnect after the transformer shall be bonded with a minimum of 2 electrodes to earth. Instead of having just a disconnect why don’t you install a main panel outside with a main breaker and do all your bonding there. Then your house panel will require that all grounds and neutrals shall be kept separate.
 

Reply to NEC 2020 Emergency Disconnect Wiring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

  • Question
The lug to use for this purpose is the Square D / Schneider Electric QO/Homeline 100 Amp Auxillary Neutral Lug Kit for Electrical Panel/Load...
Replies
2
Views
757
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top