Hi all, after considering replacing a friends old part rcd protected CU for a Wylex Hi Integrity unit, I have found the ring main to be the only ring in the house. The Continuity readings are R1 = 1.03, RN = 1.03, R2 = 1.87, these readings appear to me to be perfectly acceptable for the size of the ring. The Ze is 0.27 of which may improve slightly by changing the short 10mm Main earth to a 16mm on a TN-S system. The Measured Zs at the furthest socket outlet is 0.62, although this was using triplock and so may not be as accurate a figure as possible. The calculated Zs would be 3.17 of which is above the required 1.44 (1.15) minimum as would be using a type B 32 amp MCB. Firstly should I have much concern between the calculated and measured Zs and which should I go by, I understand it is the measured? Also as all MCB's are 30mA RCD protected, I have seen on other posts that under these circumstances a slightly higher than required Zs could be, lets say be ignored. I would just like some input and views on my findings and what others may consider apart from splitting the ring. Many thanks.