Hi all, after considering replacing a friends old part rcd protected CU for a Wylex Hi Integrity unit, I have found the ring main to be the only ring in the house. The Continuity readings are R1 = 1.03, RN = 1.03, R2 = 1.87, these readings appear to me to be perfectly acceptable for the size of the ring. The Ze is 0.27 of which may improve slightly by changing the short 10mm Main earth to a 16mm on a TN-S system. The Measured Zs at the furthest socket outlet is 0.62, although this was using triplock and so may not be as accurate a figure as possible. The calculated Zs would be 3.17 of which is above the required 1.44 (1.15) minimum as would be using a type B 32 amp MCB. Firstly should I have much concern between the calculated and measured Zs and which should I go by, I understand it is the measured? Also as all MCB's are 30mA RCD protected, I have seen on other posts that under these circumstances a slightly higher than required Zs could be, lets say be ignored. I would just like some input and views on my findings and what others may consider apart from splitting the ring. Many thanks.
 
you say R1 etc. do you mean r1 etc. where r1 is the end to end resistance of the RFC. if so, you need to divide r1+r2 by 4 when calculating Zs.
 
Normally you would calculate if there was a limitation to you getting an actual reading, always go with what your tester tells you, an if you want to check your results, calculate what you should get to what your actual results are
 
yep. if he's using r1 +r2 instead of R1+R2, his calc.will be out. i make it R1+R2 as 0.725, then add Ze.
 
Hi all, after considering replacing a friends old part rcd protected CU for a Wylex Hi Integrity unit, I have found the ring main to be the only ring in the house. The Continuity readings are R1 = 1.03, RN = 1.03, R2 = 1.87, these readings appear to me to be perfectly acceptable for the size of the ring. The Ze is 0.27 of which may improve slightly by changing the short 10mm Main earth to a 16mm on a TN-S system. The Measured Zs at the furthest socket outlet is 0.62, although this was using triplock and so may not be as accurate a figure as possible. The calculated Zs would be 3.17 of which is above the required 1.44 (1.15) minimum as would be using a type B 32 amp MCB. Firstly should I have much concern between the calculated and measured Zs and which should I go by, I understand it is the measured? Also as all MCB's are 30mA RCD protected, I have seen on other posts that under these circumstances a slightly higher than required Zs could be, lets say be ignored. I would just like some input and views on my findings and what others may consider apart from splitting the ring. Many thanks.

Just to clarify here....your redings appear as expected for an obviously large ring circuit. I'd agree that a slightly higher than permitted Zs could still be acceptable if an RCD is in place,but this would normally be when changing a type B for a C for example,or when one long spur is giving a high reading and the rest of the ring is ok.
 

Reply to Need confirmation on Zs results. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
917
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
889
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top