can anybody help me with reguards to the i2t (energy let through data) some manufactures provide a graph and others state a figure. im confused as to what value of I2t (energy let thru to use) for a given fault current when trying to calculate minimum cpc for fault currents <0.1s

I2t < s2k2

please can anyone help.
 
Last edited:
If the 3ka is your PSC at the supply then this will be used to look up the I2t rating of the mcb , but each manufacterer and mcb type is different so you'll need the mcb makers info.
 
right thankyou biff , so if my PSC at supply is 1.8kA (measured) then i would use this as my fault current when looking up the I2t on the manufactures graph.

some manufactures just supply figures for 3ka 6ka 10ka mcb rating ect (max values of i2t ) if your max PSC is only 1.8kA what figure would be used for i2t sorry if im beeing thick just confused as the data is presented in different ways.

trying to work out if a cpc has been incorectly sized. i used the adiabatic and manufactures time/current graph due to low zs and discconection time being 0.01s and it appeared fine. now when using i2t <k2s2 im not sure as to which figure i need to use for i2t if that makes any sense
 
Sounds challenging stuff , not usually done in such detail for regular work , is this for a college course ?
If your doing this stuff often i'd recommend bying the IEE design guide book , it gives working examples of the I2t calcs.
 
your right im going too deep ill just stick with the adiabatic calclations seem to work out fine

zs 0.35. i = 230/0.35 =657.14 A. k= 115. t = 0.01s (manfactures data)

so S = sqrt(657.14^x0.01) /115

= 0.57mm2 so 1.5mm2 cpc should be perfectly ok.
 
your right im going too deep ill just stick with the adiabatic calclations seem to work out fine

zs 0.35. i = 230/0.35 =657.14 A. k= 115. t = 0.01s (manfactures data)

so S = sqrt(657.14^x0.01) /115

= 0.57mm2 so 1.5mm2 cpc should be perfectly ok.

^^^ All that for 1.5 lol ?! wouldnt blame you if it was 185mm SWA at ÂŁ200 a metre lol.
Good effort on the calcs though :)
 

Reply to need help with energy let thru data in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

  • Question
word of caution, the federal electric breakers are old bits of kit. I have known them sometimes to refuse to turn back on if they are tripped or...
Replies
7
Views
707
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top