need to pick some brains. | on ElectriciansForums
Discuss need to pick some brains. in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
got some homework due in tomorrow and i can't find some of the answers anywhere in osg or regs book.
1) how do you test metal conduit for continuity?
2)what is the relationship between resistence values for live and earth cables in a ring?
how would a spur effect test readings.
3)where does it say about making good after installing cables in walls?
answers please or pages to find answers in regs book
cheers guys.
1. By carrying out an R2 test
2. In a 2.5/1.5 ring circuit the resistance end to end of cpc's will be 1.67 times as much as the lines and neutrals.
3.??
Upvote 0
I will give you some pointers as a hint but not giving answers (heard that before)
1, Regs section 6, OSG section 9, or GN3
2, OSG section 9, GN3
3, Regs section 5 560.10
Upvote 0
pritty sure after installing a cable you have to resore any fire protection around a penetration 560.10 is a rough guide i used it as a glance at the BRB. after a better look i found this 527.2
Upvote 0
sorry to be a pest lads but i'm still unsure about my 2nd question.
what is the relationship between resistence values for live and earth cables in a ring? how would a spur effect test readings?
the first part i get as the difference in conductor sizes mean different resistence values. i don't have red osg or gn3. how would a spur effect the test readings?
Upvote 0
Hi.
If you were carrying out an interconnected R1+R2 test and testing at each socket outlet then the readings would be substantially the same for all sockets that were on the ring circuit.
At the spur however the reading would be uncharacteristically higher than all the other readings due to it being spurred off the ring and not part of the original loop i.e single conductors.
Hope this makes sense to you.:)
Upvote 0
cheers lads. unfortunately home work was in before i saw this thread but now i'll know in the future so nevermind but thanks for all your help. also did my 303 fault finding and rectification practical exam yesterday and got a credit (woohoo!). 3 exams down 2 to go.
Upvote 0
Reply to need to pick some brains. in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
It was a one time ÂŁ19.99 fee. I'll be reaching out to them though to get that back. It was the only online extensive bank of questions that I...
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Electrical Courses