Neutral/Earth Fault | on ElectriciansForums
Discuss Neutral/Earth Fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
R
Reload
Does anyone have experience of neutral/earth faults and how you found it?
are you talking wiring faults or installations with appliances causing faults etc.
if to do with wiring you often find a neatral in a metal box been caught by a screw or something, and at ceiling roses a screw that caught the lampholder neutral connection on the 2nd fix stage, lots of posibilities, chase that fault with a megger!! i love fault finding find it much more interesting than the other mondane electrics!
Have you isolated which circuit has the neutral to earth fault yet, thats the starting point.
split each neutral in turn from the neutral bar and IR test it to the earth bar.
Once you have found the circuit, walk to the middle of the circuit (or where you think it is) Split the neutral (lets say its a a ceiling rose) and IR test each one to earth. You find the half of the circuit the fault is in, then just keep splitting down. This is the 'split half' tecnique, i have used it extensively with large machine control circuits
Great thanks everyone - I will investigate as you [all] described. The circuit is a radial socket cct (not installed by myself). I noticed that one of the socket circuits was not on the RCD side of the board - I tried it in the RCD side and, probably, found why the person who changed the consumer (apparently 3 years ago) had not included this cct on the RCD side; the RCD kept tripping. So, I had a look in all the sockets (metal clad 2G type) but could not find anything obvious so I guess the fault must lie within the interconnections or from the board to the first socket (of course its all hidden underfloors, walls etc along with any JBs). With this type of issue what are the possible consequences, live metalwork; MCBs not tripping in the specified times; nuisance tripping; fire hazard?
It's not bound to be a fault, any equipment plugged in may be neutral earthed anyhow, transformers on ch systems, some elv lighting systems, door bell spur off ring circuit, door entry, cctv, elv fans in bathrooms, burglar alarm.. loads of external stuff will seem earth neutral fault, old trannies trip rcd's -;)
what if they are not full trannies and just like the occasional bit of cross dressing?
sorry, couldnt resist it!:p
Reply to Neutral/Earth Fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Start with Big Clive on Youtube if you want electronic teardowns.