Having an issue with some downlights. The lights suddenly stopped working and the customer said they had no idea why! The downlights are on a downstairs ring and none of the other lights are effected. So my first thought was a problem with one of the transformers so I disconnected each transformer in turn to see if I could eliminate the one that was causing the problem (only three lights).
Removing each transformer didn't help so I disconnected the rest of the circuit from the first light so there was only one light being feed from the switch wire and fitted a new transformer. Again not working and when I tested the voltage before the transformer and it was only giving 50 volts, removed the transformer and downlight and tested it again and it gave 240 volts!

So whenever I put a demand on the circuit I lose masses of voltage... so I can only think of a broken or badly terminated neutral as the reason??!! Access is a issue in trying to track this neutral down so could I link into another lights neutral from the same ring? No other rooms are affected so this seems a logical solution. I have access for this and I can't think of a reason why it wouldn't work??!!

Suggestion please. Very new and learning. Fine with installing new stuff but fault finding and problems solving I struggle with...

Thanks
 
It's a two gang dimmer and as it was operating one side of the room fine I disregarded it but it could still be damaged on one side and not the other I guess?... so I'll change it over tomorrow quickly to see!
 
A firm believer in the principle that normally the most likely explanation is the likely suspect:

Favourite fault with downlights = burnt wiring / connectors
Favourite fault with 12v electronic selv = they fail
Favourite fault with dimmer switches = they fail

Remember also that as most dimmers found nowadays are the Triac type, not just a big resistor, they need a certain amount of load to be stable and a digital test meter is fairly useless at 'testing' them.
 
It's a two gang dimmer and as it was operating one side of the room fine I disregarded it but it could still be damaged on one side and not the other I guess?... so I'll change it over tomorrow quickly to see!
Defo worth a try, or even just temporarily bypass the dimmer to check the lights. You'll generally find that each side of a two gang dimmer is a completely separate module, so one side working has no bearing on the other side. In fact, if you have a spare dimmer module of the right size and rating, you can just replace one side.
 
Hold on guys what's all this nonsense about faulty dimmers and transformers. Take a step back. OP said the I/P to the transformer primary is only 50V. With transformer disconnected and the feed cable unloaded voltage rises to 240V, but when loaded the voltage drops to 50V again. So the fault appears to be somewhere in the main lighting final circuit.
High on my list of suspects would be a loose connection(s) (L and/or N) in a JB, connection box or ceiling rose joining or extending the feed cable to the main lighting final circuit, as there is no mention of dim lights or problems elsewhere on the final circuit.
 
Hold on guys what's all this nonsense about faulty dimmers and transformers. Take a step back. OP said the I/P to the transformer primary is only 50V. With transformer disconnected and the feed cable unloaded voltage rises to 240V, but when loaded the voltage drops to 50V again. So the fault appears to be somewhere in the main lighting final circuit.
High on my list of suspects would be a loose connection(s) (L and/or N) in a JB, connection box or ceiling rose joining or extending the feed cable to the main lighting final circuit, as there is no mention of dim lights or problems elsewhere on the final circuit.

Not sure how that eliminates the dimmer?.....The OP said no other lights on the circuit are affected....it is quite likely only the switched side of the dimmer is subject to the volt drop, which suggests dimmer to me.
As already stated the simplest test is to replace the dimmer for a on/off switch...if the problem persists you can then start testing back with a continuity or voltage tester safe in the knowledge that you are not getting any misleading readings through a dimmer.
 
Last edited by a moderator:
6 tests you need to do:
No load
  • L > N
  • L > E
  • N > E
On load
  • L > N
  • L > E
  • N > E
This will indicate if there’s a high resistance joint and more importantly which leg L or N.
 
Last edited by a moderator:
I had this the other week and tracked it down to a netural in a Jb pinched to hard when removing sleeving..
Thus it was semi floating and displayed all the symtoms you have said..
 
Last edited by a moderator:
I think maybe some people are forgetting one little thing, here: The phrase 'it STOPPED working'. ie, it did use to work and then stopped for no explanation.

Unless a cable has been in a jb for so many years it's evolved and grown legs, it's unlikely to be an undisturbed cable suddenly causing problems (assumes it was jointed tight and correctly in the first place, rodents etc granted). So what we have left are components that we know DO fail - filaments and electronics.
 

Reply to Neutral issue me thinks!!! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
856
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
689
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top