Having an issue with some downlights. The lights suddenly stopped working and the customer said they had no idea why! The downlights are on a downstairs ring and none of the other lights are effected. So my first thought was a problem with one of the transformers so I disconnected each transformer in turn to see if I could eliminate the one that was causing the problem (only three lights).
Removing each transformer didn't help so I disconnected the rest of the circuit from the first light so there was only one light being feed from the switch wire and fitted a new transformer. Again not working and when I tested the voltage before the transformer and it was only giving 50 volts, removed the transformer and downlight and tested it again and it gave 240 volts!

So whenever I put a demand on the circuit I lose masses of voltage... so I can only think of a broken or badly terminated neutral as the reason??!! Access is a issue in trying to track this neutral down so could I link into another lights neutral from the same ring? No other rooms are affected so this seems a logical solution. I have access for this and I can't think of a reason why it wouldn't work??!!

Suggestion please. Very new and learning. Fine with installing new stuff but fault finding and problems solving I struggle with...

Thanks
 
Hi Daniel,
Its not good practise to feed lights from a ring main,not your doing but if possible it would be best to supply the
lights from the lighting breaker,if you link a lighting nuetral to the downlights you could cause
crossed nuetral to the ring which would trip any rcd.
 
Sorry if I wasn't clear but I'm talking about using a neutral from the exsisting lighting ring not the ring main! This would be ok I take it?
 
If you start testing the circuit as if it were a new circuit, that should throw up some odd results somewhere along the way which will give you a good indication. Given that the problem is with the downlighters that will give you a starting point.
Try to avoid putting 500v across live and neutral though...
 
Yes that will be fine,sorry when you said downstairs ring i thought you meant ring main,
maybe its me but i refer to rings as ring mains and lights as lighting circuits.
you will be fine,sometimes its easier to run a new cable than trying to find
the fault,just remember to disconnect the original cable.
 
Using the exsisting live feed and putting in a new neutral from the downlights to the junction box where the other lights on the same lighting ring run to?
 
Again not working and when I tested the voltage before the transformer and it was only giving 50 volts, removed the transformer and downlight and tested it again and it gave 240 volts!

So whenever I put a demand on the circuit I lose masses of voltage... so I can only think of a broken or badly terminated neutral as the reason??!!

If you're measuring the voltage between line and neutral, why do you think that it's a neutral fault? Surely it could just as well be a fault in the line?
 
you could seperate section and do an an R1 R2 then an R2 Rn....see if the results are similar (assuming it is t&w)...what size cable is it? 1mm?....1.5....?....
 
Last edited by a moderator:
As a rule in most UK domestic installations you should always get zero volts if you test between neutral and earth (CPC). If you get a voltage (>1volt) between neutral and earth even when the circuit is live and under load then you have a neutral problem.

A drop in voltage (L-N) could indicate a missing or partially missing live or neutral.
 
It's a two gang dimmer and as it was operating one side of the room fine I disregarded it but it could still be damaged on one side and not the other I guess?... so I'll change it over tomorrow quickly to see!
 
A firm believer in the principle that normally the most likely explanation is the likely suspect:

Favourite fault with downlights = burnt wiring / connectors
Favourite fault with 12v electronic selv = they fail
Favourite fault with dimmer switches = they fail

Remember also that as most dimmers found nowadays are the Triac type, not just a big resistor, they need a certain amount of load to be stable and a digital test meter is fairly useless at 'testing' them.
 
It's a two gang dimmer and as it was operating one side of the room fine I disregarded it but it could still be damaged on one side and not the other I guess?... so I'll change it over tomorrow quickly to see!
Defo worth a try, or even just temporarily bypass the dimmer to check the lights. You'll generally find that each side of a two gang dimmer is a completely separate module, so one side working has no bearing on the other side. In fact, if you have a spare dimmer module of the right size and rating, you can just replace one side.
 
Hold on guys what's all this nonsense about faulty dimmers and transformers. Take a step back. OP said the I/P to the transformer primary is only 50V. With transformer disconnected and the feed cable unloaded voltage rises to 240V, but when loaded the voltage drops to 50V again. So the fault appears to be somewhere in the main lighting final circuit.
High on my list of suspects would be a loose connection(s) (L and/or N) in a JB, connection box or ceiling rose joining or extending the feed cable to the main lighting final circuit, as there is no mention of dim lights or problems elsewhere on the final circuit.
 
Hold on guys what's all this nonsense about faulty dimmers and transformers. Take a step back. OP said the I/P to the transformer primary is only 50V. With transformer disconnected and the feed cable unloaded voltage rises to 240V, but when loaded the voltage drops to 50V again. So the fault appears to be somewhere in the main lighting final circuit.
High on my list of suspects would be a loose connection(s) (L and/or N) in a JB, connection box or ceiling rose joining or extending the feed cable to the main lighting final circuit, as there is no mention of dim lights or problems elsewhere on the final circuit.

Not sure how that eliminates the dimmer?.....The OP said no other lights on the circuit are affected....it is quite likely only the switched side of the dimmer is subject to the volt drop, which suggests dimmer to me.
As already stated the simplest test is to replace the dimmer for a on/off switch...if the problem persists you can then start testing back with a continuity or voltage tester safe in the knowledge that you are not getting any misleading readings through a dimmer.
 
Last edited by a moderator:
6 tests you need to do:
No load
  • L > N
  • L > E
  • N > E
On load
  • L > N
  • L > E
  • N > E
This will indicate if there’s a high resistance joint and more importantly which leg L or N.
 
Last edited by a moderator:
I had this the other week and tracked it down to a netural in a Jb pinched to hard when removing sleeving..
Thus it was semi floating and displayed all the symtoms you have said..
 
Last edited by a moderator:
I think maybe some people are forgetting one little thing, here: The phrase 'it STOPPED working'. ie, it did use to work and then stopped for no explanation.

Unless a cable has been in a jb for so many years it's evolved and grown legs, it's unlikely to be an undisturbed cable suddenly causing problems (assumes it was jointed tight and correctly in the first place, rodents etc granted). So what we have left are components that we know DO fail - filaments and electronics.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Neutral issue me thinks!!!
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
Danielwareham,
Last reply from
HandySparks,
Replies
25
Views
2,498

Advert

Back
Top