What current does the neutral take on a 3 phase system? For example if each line conductor pulls 100A, what does the neutral pull? Obviously not 300A, Bit confused, don't really work on 3 phase much.
 
If each line conductor was drawing exactly 100A, there wouldn't be any current in the neutral conductor as all the phases are balanced.

Neutral current presents itself only when phases are unbalanced, the magnitude depends on how unbalanced they are.
 
Thanks guys, often wondered, but never asked. Glad I did now. So if an installation was severely imbalanced I guess this could cause over heating in the neutral conductor?
 
When an installation is designed the board is designed as balanced on all phases so sa the lads say no current in nuetral but in are works main kitchen area a re disgn of the kitchen which didn't include any design people cos of cost has left the board unbalanced on all phases but there is no over heating or damage to the nuetral
 
Neutral current can never exceed the current of 1 phase which is why neutral conductor is usually same size as phase. Single phase
is as out of balance as you can get(100A Line = 100A Neutral). Currrent going into the neutral from 3 phases cancel each other out.
ie if all phases are balanced and put same current into neutral conductor they cancel each other out.
 
Thanks guys, often wondered, but never asked. Glad I did now. So if an installation was severely imbalanced I guess this could cause over heating in the neutral conductor?

Excluding all harmonics etc or loose connections, if you load up 1ph with 100amp and left ph2 and 3 empty your N current would be 100amps, adding load to ph2 or 3 will reduce the neutral current so as long as the neutral is the same csa as the phase conductor it will if the installation is designed correctly never overload with inbalance.
Many newby's get the impression that 100amps per phase may in extreme unbalanced situe put 300amp on the Neutral which isn't the case.
 

Reply to Neutral Loading in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

For a TN system neutral is deemed at earth potential.
Replies
6
Views
345
https://sravivarman.com/technical-articles/parallel-operation-of-thyristors/ Series resistor, or bigger series resistor, needed?
Replies
1
Views
150

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top