Favour for a mate has turned into a nightmare. Really appreciate any comments on the below!
Was asked to look at some sockets which have apparently been "sparking".......
17th edition board. 100amp/30ma RCD as main switch and only additional protection for 11 circuits. Unsure if that conforms with BS EN 60947-3?!
Ze 0.32. TNS
Bonding appears good, only ohm tested across exposed metal work couldn't find actual straps, but it leaves from the CU.
Unable to perform a Zs at 4 sockets from 8, Error 4 on my fluke. >50v N->Earth. Rest of circuit tests no issue. 2.5mm radial.
L->E 240v
L->N 240v
N->E 30v(ish)
So i'm assuming we have a poor neutral joint somewhere between the good and bad sockets...why is the RCD not tripping when load is applied to these sockets?!
After taking the entire circuit apart i couldn't find the smoking gun, so now i'm working on the assumption a joint in the ceiling.... At which point I threw in the towel isolated the circuit and said i'd have to come back ASAP.
It also looks likely that that 2x B16 radials use to be a ring (flagging on cables with tape in CU). Would that change anything?
Am i missing anything here? neutral to earth faults always mess with my head.
Any advice will be helpful. Constructive or otherwise!!
Was asked to look at some sockets which have apparently been "sparking".......
17th edition board. 100amp/30ma RCD as main switch and only additional protection for 11 circuits. Unsure if that conforms with BS EN 60947-3?!
Ze 0.32. TNS
Bonding appears good, only ohm tested across exposed metal work couldn't find actual straps, but it leaves from the CU.
Unable to perform a Zs at 4 sockets from 8, Error 4 on my fluke. >50v N->Earth. Rest of circuit tests no issue. 2.5mm radial.
L->E 240v
L->N 240v
N->E 30v(ish)
So i'm assuming we have a poor neutral joint somewhere between the good and bad sockets...why is the RCD not tripping when load is applied to these sockets?!
After taking the entire circuit apart i couldn't find the smoking gun, so now i'm working on the assumption a joint in the ceiling.... At which point I threw in the towel isolated the circuit and said i'd have to come back ASAP.
It also looks likely that that 2x B16 radials use to be a ring (flagging on cables with tape in CU). Would that change anything?
Am i missing anything here? neutral to earth faults always mess with my head.
Any advice will be helpful. Constructive or otherwise!!