I think you mean insulation resistance not resistance there different.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Neutral to Earth in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
Ok, i feel really stupid now.I think you mean insulation resistance not resistance there different.
Oh i like it!View attachment 59486
now here is where it gets a little complicated. give me 5 to edit
Oh i like it!
[automerge]1594837207[/automerge]
Not sure of the R bond though
[automerge]1594837229[/automerge]
loving the diagram, much respect
I feel a you tube video coming. LolWear some safety glasses, a small mistake could lead to exploding resistors.
Max Zs is 1667 ohms on a 30mA which is touch voltage of 50V.
Where the maximum Zs value for a protective device cannot be satisfied in a TN system, Regulation 531.3. 1 permits an RCD (including an RCBO) to be used to provide automatic disconnection of the supply. Table 41.5 would therefore apply and the maximum tablulated Zs value for a 30mA RCD is 1667 ohmsFor a TN system it is 7667 ohms not 1667, that is for TT systems.
neutral is connected to earth
Also Neutral is a live conductor, and will have 230V passing through it.