Crosswire
Went to a house today where outside lights were tripping the rcd.
1.5 swa from house to ip box containing timer, which controlled a few sets of lights - wall lights, light in bin store, and drive over lights.
Each group of lights had one cable from ip box , all fairly standard stuff.
Anyway split all lights apart and touch them on one by one to live feed to find faulty lights quickly ( was the drive over lights full of water, but this is not the point) .When I touched the wall light on I got a belt off the neutral which was hanging loose and brushed my hand !
Seperated cable and found it did ONE wall light (230v ES).
When lamp was put in got 230v on neutral .
Tried three different testers all showed 230v
Meggered cables all perfect readings
Connected this light on it's own to feed and energised - didn't trip breaker or RCD and light worked fine!
Went to board tested neutral and earth bars - 0 v.
It was my understanding that the resistance of the lamp should cause the voltage to drop to 0v across the load, and the neutral should be a return path for current, not voltage!
Anyone explain this ?
*Disclaimer * Please no-one post about 'safe isolation procedure' etc.. I know what I did is not textbook, but it is QUICK. The point of this thread is the strange voltage on the neutral, and nothing else. Cheers!
1.5 swa from house to ip box containing timer, which controlled a few sets of lights - wall lights, light in bin store, and drive over lights.
Each group of lights had one cable from ip box , all fairly standard stuff.
Anyway split all lights apart and touch them on one by one to live feed to find faulty lights quickly ( was the drive over lights full of water, but this is not the point) .When I touched the wall light on I got a belt off the neutral which was hanging loose and brushed my hand !
Seperated cable and found it did ONE wall light (230v ES).
When lamp was put in got 230v on neutral .
Tried three different testers all showed 230v
Meggered cables all perfect readings
Connected this light on it's own to feed and energised - didn't trip breaker or RCD and light worked fine!
Went to board tested neutral and earth bars - 0 v.
It was my understanding that the resistance of the lamp should cause the voltage to drop to 0v across the load, and the neutral should be a return path for current, not voltage!
Anyone explain this ?
*Disclaimer * Please no-one post about 'safe isolation procedure' etc.. I know what I did is not textbook, but it is QUICK. The point of this thread is the strange voltage on the neutral, and nothing else. Cheers!