asked to price a new build on the plans it shows two flats ground floor eith own front door. two flats first floor with a door onto stairs then two entrance doors, then top floor flat is size of whole building with own front door on ground floor.
ground floor entrance all have own door, the question is what to do regarding smoke alarms? do they need to be in the stairs to the first floor flats.
the other thing is their will not be a landloards supply so what do you do regarding smoke alarms in comunal areas without one?
any thoughts?
Oy Vey.
Okay, HMO 101.
It's an HMO. That is, a building with more than one family/dwelling.
That means it has to comply with certain rules, regulations, and requirements, set out for HMO's.
Key among those if fire safety - covered off in Building Regs, Regulatory Reform (Fire Safety) Order, and various other bits of legislation.
What this means is that there are requirements placed on both the landlord (or owner) AND on tenants (or occupiers).
Landlord is overall responsible for Fire Safety - which at a basic means he will need to prove he has taken all reasonable steps to reduce or eliminate risk from fire. Commonly, this means fitting some sort of fire detection system, possibly some emergency lighting, and possibly other fire measures too.
You tell us that there are at least three floors to this building. That tells me right away that any smoke detection/fire alarm will require to comply with BS5839-6, Grade A. If there is an independent fire escape fitted to the exterior of the building, and accessible from all flats, and LD3 category system will be sufficient, and if not, LD2.
Essentially, what that, in turn means, is you need a "proper" fire alarm system, and not just smoke detectors. That system should have a permanent independent supply - e.g. from a landlord's board, and dedicated solely to the fire alarm, including wired in fire resiting cable from board to spur. Spur should also be such that it cannot be tampered with - e.g. needs a tool to isolate, or is inaccessible to casual tampering.
I don't see how, to be honest, you're going to get away without a communal/landlord's supply - at some point you're going to have issues without it - communal lighting, emergency lighting (which is likely with five separate tenants), and a fire alarm - for the sake of sticking in a four way board, it's not worth trying to go without.