I've tried to download & read a copy of BS 6891:2005 before now, you can but they won't to add some iffey documents as well.
Best quotation I found was on Voltimum web site; BS 6891:2005 Installation of low pressure gas pipework in domestic premises, clause 8.16.2 states that gas installation pipes must be spaced at least 150mm away from electricity meters, controls, electrical switches or sockets, distribution boards or consumer units.
And Regulation 528.3.3 (BS7671) requires that where an electrical service is installed in proximity to a non-electrical service, it must be arranged so that any foreseeable operation carried out on the other service will not cause damage to the electrical service or the converse. This can be achieved by suitable spacing or mechanical or thermal shielding.
Also referred to in OSG.So as Dillb says, who's the inspector? Can you move the gas pipe?