I will be fitting a new CCU in a house that has a TT installation. Going to look at the job tomorrow evening but just been doing a bit of reading up so I know what to check for - particularly as the homeowner mentioned he was a bit unsure about the bonding.

I'm pretty sure it will have an earth conductor and I'm really hoping all the main bonding conductors are satisfactory. From what I've read I suspect, what he might mean is, that the supplementary bonding is missing.

My understanding is that this is acceptable if all final circuits in the installation are protected by RCD/s and the maximum disconnection times are satisfied and...

"All extraneous-conductive-parts of the location are effectively connected to the protective equipotential bonding according to Regulation 411.3.1.2"

Just so I'm clear, does this last bit mean that if there is "main bonding" to the water installation pipes and the central heating system (those items most likely found in the bathroom) then supplementary bonding is not required?

Anything else unusual I should be looking for whilst I'm there? :confused:

Cheers for your help

Rich
 
think you just about got it sussed mate. looks good to me.
 
Thanks for the confirmation telectrix :D

Can I just check as well regarding the RCDs --> Split load CCU, 1x 100mA, 1x 30mA

On the 30mA - socket outlets and "locations containing a bath or shower". What am I looking for in the bathroom? Shaver points? Electric heaters? (I assume the ceiling lighting isn't included in this).

Everything else on the 100mA.
 
Cheers nick611. So basically I just need to check that there's main bonding to the water and gas service pipes.
 
Thanks for the confirmation telectrix :D

Can I just check as well regarding the RCDs --> Split load CCU, 1x 100mA, 1x 30mA

On the 30mA - socket outlets and "locations containing a bath or shower". What am I looking for in the bathroom? Shaver points? Electric heaters? (I assume the ceiling lighting isn't included in this).

Everything else on the 100mA.
nope. both RCDs need to be 30mA
 
100ma dosent cover cables in walls,socket outlets or any circuit in bathroom,its 30ma on everthing now.
 
every circuit has to have 30mA protection , anything, including lights, in a bathroom, any circuit with cables buried in walls less than 50mmm deep, every socket, even the cat flap and the bog seat, if they're electric.
 
wylex 10 way 17th split board loaded with 8MCBs, £65+vat, electric center
 
check the stake as well,make sure its protected at the connection and labelled and below 200ohms.
 
OK, got it. I'd read the bit in the OSG about TT earthed steel conduit installations. Now I don't know that this house has that but I guess I can check in a couple of sockets to see if there is any conduit running to them. Make life easier if there isn't!
 

Reply to the thread, titled "New CCU in TT installation - bonding question" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New CCU in TT installation - bonding question
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Stormflex,
Last reply from
Stormflex,
Replies
11
Views
2,821

Advert

Back
Top