Stormflex
I will be fitting a new CCU in a house that has a TT installation. Going to look at the job tomorrow evening but just been doing a bit of reading up so I know what to check for - particularly as the homeowner mentioned he was a bit unsure about the bonding.
I'm pretty sure it will have an earth conductor and I'm really hoping all the main bonding conductors are satisfactory. From what I've read I suspect, what he might mean is, that the supplementary bonding is missing.
My understanding is that this is acceptable if all final circuits in the installation are protected by RCD/s and the maximum disconnection times are satisfied and...
"All extraneous-conductive-parts of the location are effectively connected to the protective equipotential bonding according to Regulation 411.3.1.2"
Just so I'm clear, does this last bit mean that if there is "main bonding" to the water installation pipes and the central heating system (those items most likely found in the bathroom) then supplementary bonding is not required?
Anything else unusual I should be looking for whilst I'm there?
Cheers for your help
Rich
I'm pretty sure it will have an earth conductor and I'm really hoping all the main bonding conductors are satisfactory. From what I've read I suspect, what he might mean is, that the supplementary bonding is missing.
My understanding is that this is acceptable if all final circuits in the installation are protected by RCD/s and the maximum disconnection times are satisfied and...
"All extraneous-conductive-parts of the location are effectively connected to the protective equipotential bonding according to Regulation 411.3.1.2"
Just so I'm clear, does this last bit mean that if there is "main bonding" to the water installation pipes and the central heating system (those items most likely found in the bathroom) then supplementary bonding is not required?
Anything else unusual I should be looking for whilst I'm there?
Cheers for your help
Rich