V

Victorcrane

Hey guys. Just interested in your opinions on this one before I speak to my NIC field engineer. I have a customer who wants a new ccu installed but his property is rather old and he has the classic 2 core twin lighting arrangement so no earths whatsoever on the lighting.

I did the initial pir and informed the customer of the situation and that it didn't meet regs and would be deemed unsatisfactory but he insists he wants a new ccu fitting but without further remedial works i.e. the installation of cpc for the lighting.

Because I've not come across this particular situation before I'm not sure exactly where I stand. Ordinarily when I do works I bring absolutely everything up to current code as a matter of course, but here this isn't possible. I know I can't force anyone to have the issue corrected but should I replace the ccu for him knowing that the circuit isn't fit for purpose? I'm not making it any worse I guess....

Ideas?
 
you can replace the CU, make sure all lighting fittings and switches are class 2. note on your EICand label CU something like " no cpc on lighting. only class 2 fittings to be used . you will probably find thet the lugs in the switches are nylon to prevent the pins becoming live in the event of a fault.
 
Many thanks telectrix I was hoping that may well be the case. I'm quite new to NIC stuff so I'm still learning what I am and am not allowed to do. Mind you from the last meeting I had with my NIC guy it seems I can do absolutely anything so long as I note it on the paperwork! :)
 

Reply to New ccu requirements in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Except where provided by the EV charging equipment, protection against DC fault currents shall be provided by: (i) an RCD Type B, or (ii) an RCD...
Replies
5
Views
942
  • Question
What I find a little bit interesting is that there was an era of MFT's e.g. Robin, early Kewtech that tried to do non-trip loop tests using D-Lok...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top