Rather than have a temporary building supply my customer has agreed with Southern Electricity for them to cut and extend his current supply to a cabin at the rear of his house which is being demolished.
I am planning on installing a small CU with 30mA RCD main switch and an earth stake since there will be no gas or water to bond to, my thinking for this is so that it can also meet the requirements of a TT site supply and also for if it is fed from the CU in the new house in the future. It’s a partial self build project which could take a long time.

Re: the buried earthing conductor to the stake (a 5/8 1200), after looking at the Regs and GN’s 1 and 8, I'm a little confused but assume I need 16mm2 (even with mechanical and corrosion protection)?

My customer will install a surface mounted meter box on the front of his cabin.

Just wanted confirmation that this was the best way or not?! (Originally I was going to install a split load CU with 2 RCD’s instead of on the main switch and an earth stake)
It’s currently TNS. I’m also wondering if Southern Electric will change it to TNCS.
 
Re: New connection direct to cabin whilst house is demolished scenario - advice requi

Rather than have a temporary building supply my customer has agreed with Southern Electricity for them to cut and extend his current supply to a cabin at the rear of his house which is being demolished.
I am planning on installing a small CU with 30mA RCD main switch and an earth stake since there will be no gas or water to bond to, my thinking for this is so that it can also meet the requirements of a TT site supply and also for if it is fed from the CU in the new house in the future. It’s a partial self build project which could take a long time.

If you have a TN-S supply why are you wanting to downgrade it to a TT

Re: the buried earthing conductor to the stake (a 5/8 1200), after looking at the Regs and GN’s 1 and 8, I'm a little confused but assume I need 16mm2 (even with mechanical and corrosion protection)?

Assume this is an earthing conductor we are talking about .....have a look at reg 543.1.1 as you have a TN-S supply

My customer will install a surface mounted meter box on the front of his cabin.

Just wanted confirmation that this was the best way or not?! (Originally I was going to install a split load CU with 2 RCD’s instead of on the main switch and an earth stake)
It’s currently TNS. I’m also wondering if Southern Electric will change it to TNCS.

They may undeed upgrade to the TNC-S but you will have to ask them this
 
Re: New connection direct to cabin whilst house is demolished scenario - advice requi

Initially as there is no main bonding if there was a fault with the supply earth so thought about using an earth stake and after research because of what I have read on the bottom of page 6 of the link below - see part 3.1 - although I personally haven't found any thing specific about this in the Regs etc


electrical.------.org/wiring-matters/16/earthing-questions.cfm?type=pdf
 
Re: New connection direct to cabin whilst house is demolished scenario - advice requi

Sorry mate it is my age so you'll have to bear with me a little, if the DNO have agreed to transfer their TN-S supply from the house to the Cabin, even be it temporary, then they are still liable to maintain that earth for the customer.

As you said in your original post there is no gas or water services, which IMO opinion is, if not illigal for a dwelling is not very comfortable, and providing the cabin itself is not metal, there is no need for bonding anything.
 

Reply to New connection direct to cabin whilst house is demolished scenario - advice required in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top