I believe we should consider a big difference between a lightning strike and over voltage, since they are not the same. An SPD is for over voltage and will not protect against a direct strike or one very close by. I recently attended a course for SPD’s and have an interest on TT (there are many locally). The recommendation was a type 1 for incoming overhead lines. I’ll dig out the detail and put it here.
 
Why only one rod? Personally I aim to get at least two 2.4m rods in suitably spaced for a TT system.

Really? I'm interested in your thinking? Do you fit the second rod because the first reading was too high or just your standard practice. I had considered doing this but depending on the Ze measurement alone. I'm going back to a couple of properties in the summer to test again - my measurements where sub 40 ohms recently.
 
Really? I'm interested in your thinking?
Do you fit the second rod because the first readingwas too high or just yourstandard practice.

The general idea is to get the Ra as low as possible. As you increase depth the reduction in Ra is not linear, so 2x 2.4m rods will give a lower Ra than 1x 4.8m rod.
It has become my standard practice, the first reading is always too high in my opinion because I know it can be improved by adding a second rod.
 
Really? I'm interested in your thinking? Do you fit the second rod because the first reading was too high or just your standard practice. I had considered doing this but depending on the Ze measurement alone. I'm going back to a couple of properties in the summer to test again - my measurements where sub 40 ohms recently.

The correct way to do it would be a cost v benefit analysis. Is another rod viable? Is another rod worth the additional cost in terms of improved earth loop impedance.
 
The general idea is to get the Ra as low as possible. As you increase depth the reduction in Ra is not linear, so 2x 2.4m rods will give a lower Ra than 1x 4.8m rod.
It has become my standard practice, the first reading is always too high in my opinion because I know it can be improved by adding a second rod.

Interesting. Do you connect the rods together then measure Ra or do you measure each rod separately and record the highest reading?
 
The correct way to do it would be a cost v benefit analysis. Is another rod viable? Is another rod worth the additional cost in terms of improved earth loop impedance.


The 'correct' way to do it is carry out soil resistivity testing and chemical analysis then design an earth electrode system from that.

The Ops situation appears to be domestic, so the cost of putting in two rods over one is relatively small, the benefit is chiefly a reduced Ra (approx half) with greater stability and redundancy.

Even greater stability could be achieved by driving a single rod to 4.8m, but the Ra will not be reduced by a lot less than half.
 
Interesting. Do you connect the rods together then measure Ra or do you measure each rod separately and record the highest reading?

I measure each rod seperately and record the result and then measure the complete network of rods together to establish Ra.
 
I would either measure both rods together using the Ze method, or measure separately, either using Ze or rod tester, then calculate resistance in parallel.
 
I would either measure both rods together using the Ze method, or measure separately, either using Ze or rod tester, then calculate resistance in parallel.

Resistance in parallel calculation doesn't necessarily yield the correct answer, the interaction of the multiple electrides has an effect.
 

Reply to New consumer unit on TT installation - earthing and SPD queries in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
509
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
979
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
909

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
3K
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top